Two wire thermostat on 4 wire electric baseboard heating
#1
Member
Thread Starter
Join Date: Dec 2020
Location: United States
Posts: 7
Received 0 Votes
on
0 Posts
Two wire thermostat on 4 wire electric baseboard heating
Hi, I am trying to replace my old mechanical thermostat for my electric baseboard heating so that I can have better control over the set temperature. I remove the old thermostat and disconnected the wires and there were 4 wires coming from the wall-two white and two black. The thermostat I bought is a Honeywell rlv3120 which only has two wires coming out the back. Can I wire this thermostat up to my current wires and if so how would I do it? If I can't, then do I need to buy a different thermostat or do I just have to stick with my old mechanical thermostat? Thank you for your help!
#2
Provided you meet the following condition, it can be used.
The RLV3120 thermostat CANNOT be used with a resistive load under 0.83, a resistive load over 8.3 a system driven by a contactor or a relay (inductive load), a fan-forced heating system (e.g. : fan-forced convector) or a central heating system.
You connect the white wires together and connect the thermostat to the two black wires.
The RLV3120 thermostat CANNOT be used with a resistive load under 0.83, a resistive load over 8.3 a system driven by a contactor or a relay (inductive load), a fan-forced heating system (e.g. : fan-forced convector) or a central heating system.
You connect the white wires together and connect the thermostat to the two black wires.
#7
Yes....you would see a spark.
You should have the breaker off before making any wire changes.
That thermostat is limited to a maximum of 8.3amps @ 240v which is 2000 watts of heater.
You should have the breaker off before making any wire changes.
That thermostat is limited to a maximum of 8.3amps @ 240v which is 2000 watts of heater.
#8
Member
Thread Starter
Join Date: Dec 2020
Location: United States
Posts: 7
Received 0 Votes
on
0 Posts
I had the breaker off when I was making the wire changes but after I turned it on was when I saw the spark. I guess I will probably need a higher rated them thermostat. Any recommendations on thermostats?
#9
You picked a digital thermostat.... is that what you want ?
Have you calculated how much wattage you have in heat strips ?
Just add the linear footage and let us know.
The Honeywell line pro stat is good for 3600 watts.
Have you calculated how much wattage you have in heat strips ?
Just add the linear footage and let us know.
The Honeywell line pro stat is good for 3600 watts.
#12
Member
Thread Starter
Join Date: Dec 2020
Location: United States
Posts: 7
Received 0 Votes
on
0 Posts
I have two separate baseboard heaters. Wasn't able to measure their exact length as I am not home but that is about what I estimate them to be. On a side note, are in wall heats like from cadet more efficient than electric baseboard?
#15
Electric baseboards are slow acting heaters. Once they get warm they offer continuous heat.
A wall heater with a fan may heat the room quicker.
There is no loss with either type of heater so neither one is more efficient.... just maybe faster acting.
A wall heater with a fan may heat the room quicker.
There is no loss with either type of heater so neither one is more efficient.... just maybe faster acting.