Two wire thermostat on 4 wire electric baseboard heating

Reply

  #1  
Old 12-20-20, 07:17 AM
T
Member
Thread Starter
Join Date: Dec 2020
Location: United States
Posts: 7
Received 0 Votes on 0 Posts
Two wire thermostat on 4 wire electric baseboard heating

Hi, I am trying to replace my old mechanical thermostat for my electric baseboard heating so that I can have better control over the set temperature. I remove the old thermostat and disconnected the wires and there were 4 wires coming from the wall-two white and two black. The thermostat I bought is a Honeywell rlv3120 which only has two wires coming out the back. Can I wire this thermostat up to my current wires and if so how would I do it? If I can't, then do I need to buy a different thermostat or do I just have to stick with my old mechanical thermostat? Thank you for your help!
 
  #2  
Old 12-20-20, 07:22 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,719
Received 295 Votes on 254 Posts
Provided you meet the following condition, it can be used.
The RLV3120 thermostat CANNOT be used with a resistive load under 0.83, a resistive load over 8.3 a system driven by a contactor or a relay (inductive load), a fan-forced heating system (e.g. : fan-forced convector) or a central heating system.

You connect the white wires together and connect the thermostat to the two black wires.
 
  #3  
Old 12-20-20, 07:34 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: United States
Posts: 4,956
Received 88 Votes on 83 Posts
Hi, how many ft. of BB do you have?
Geo 🇺🇸
 
  #4  
Old 12-20-20, 09:28 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,649
Received 48 Votes on 43 Posts
If 240v you likely need a 4 wire/2 pole thermostat with "off" as it functions as a disconnect.
 
  #5  
Old 12-20-20, 10:08 AM
T
Member
Thread Starter
Join Date: Dec 2020
Location: United States
Posts: 7
Received 0 Votes on 0 Posts
I think it is a 240v because it is on a 20amp breaker. Do you have any recommendations for a good 4 wire/2 pole thermostat?
 
  #6  
Old 12-20-20, 10:11 AM
T
Member
Thread Starter
Join Date: Dec 2020
Location: United States
Posts: 7
Received 0 Votes on 0 Posts
I tried connecting the two wires together and the black wires to the thermostat but it sparked and I turned off the breaker.
 
  #7  
Old 12-20-20, 10:14 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,786
Received 1,324 Votes on 1,224 Posts
Yes....you would see a spark.
You should have the breaker off before making any wire changes.

That thermostat is limited to a maximum of 8.3amps @ 240v which is 2000 watts of heater.
 
  #8  
Old 12-20-20, 11:14 AM
T
Member
Thread Starter
Join Date: Dec 2020
Location: United States
Posts: 7
Received 0 Votes on 0 Posts
I had the breaker off when I was making the wire changes but after I turned it on was when I saw the spark. I guess I will probably need a higher rated them thermostat. Any recommendations on thermostats?
 
  #9  
Old 12-20-20, 11:40 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,786
Received 1,324 Votes on 1,224 Posts
You picked a digital thermostat.... is that what you want ?
Have you calculated how much wattage you have in heat strips ?
Just add the linear footage and let us know.

The Honeywell line pro stat is good for 3600 watts.
 
  #10  
Old 12-20-20, 03:54 PM
T
Member
Thread Starter
Join Date: Dec 2020
Location: United States
Posts: 7
Received 0 Votes on 0 Posts
It is probably about 20 linear feet
 
  #11  
Old 12-20-20, 04:04 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,786
Received 1,324 Votes on 1,224 Posts
That's close to 4500 watts. That would be a well loaded 20A 240v circuit.
 
  #12  
Old 12-20-20, 04:42 PM
T
Member
Thread Starter
Join Date: Dec 2020
Location: United States
Posts: 7
Received 0 Votes on 0 Posts
I have two separate baseboard heaters. Wasn't able to measure their exact length as I am not home but that is about what I estimate them to be. On a side note, are in wall heats like from cadet more efficient than electric baseboard?
 
  #13  
Old 12-20-20, 05:10 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,786
Received 1,324 Votes on 1,224 Posts
All electric heaters are 100% efficient. Every watt of heat is delivered into the house.
 
  #14  
Old 12-20-20, 06:36 PM
T
Member
Thread Starter
Join Date: Dec 2020
Location: United States
Posts: 7
Received 0 Votes on 0 Posts
I have old baseboard heaters. Would updating them to newer ones help me reduce my electric costs or would switching to wall heaters be better?
 
  #15  
Old 12-20-20, 07:40 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,786
Received 1,324 Votes on 1,224 Posts
Electric baseboards are slow acting heaters. Once they get warm they offer continuous heat.
A wall heater with a fan may heat the room quicker.

There is no loss with either type of heater so neither one is more efficient.... just maybe faster acting.
 
 