Subpanel question

Am I missing something because I don't see where the neutral bars are bonded?

 
  #2  
Old 01-04-21, 05:37 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,514
Received 125 Votes on 99 Posts
Possibly it's a subpanel. There should be a first disconnect where the neutral is bonded.
 
  #3  
Old 01-04-21, 06:21 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,734
Received 300 Votes on 257 Posts
They are bonded from below. You can see part of the cross bar between the hot bus bars at the top just below the main breaker.
 
  #4  
Old 01-04-21, 07:15 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,808
Received 253 Votes on 221 Posts
Joed is correct. The neutral bars are bonded with a bar that goes behind the hot bus bars.

The larger neutral wire should not be connected to the ground bar to the upper left.

Also, it appears that somebody forgot the bushing on the main feeder pipe.
 
  #5  
Old 01-04-21, 09:05 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,514
Received 125 Votes on 99 Posts
When asking about the neutral bars being bonded I think of the bonding to ground, not that the two neutral bars are interconnected.
I believe that large white wire is being used to bond the neutral bar to ground. Unless I'm not seeing where that wire goes correctly.
The need of bushing on the pvc fitting is debatable.
 

Last edited by pattenp; 01-04-21 at 09:25 PM.
  #6  
Old 01-04-21, 09:54 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,936
Received 1,351 Votes on 1,249 Posts
That "white" wire connecting to the left hand ground bar is the ground wrap from the 60A 240v circuit in the bottom right. It should have been left bare or taped green.
 
  #7  
Old 01-05-21, 05:52 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,514
Received 125 Votes on 99 Posts
Yes, that white appears to be the extension of the ground for the 60A circuit. My question is, is this a subpanel since it has a 4 wire feed with the neutral bond being ahead of this panel at a separate disconnect? Otherwise if this panel is the first disconnect I'm not seeing the neutral bond.
The OP needs to clarify the question about the neutral bar bonding. Whether between the two bars or to the panel.
 
  #8  
Old 01-05-21, 04:37 PM
A
Member
Thread Starter
Join Date: Apr 2020
Posts: 9
Received 0 Votes on 0 Posts
Yes it is a sub panel and the white wire is the ground from the range which has since been taped green.
 
  #9  
Old 01-05-21, 04:41 PM
A
Member
Thread Starter
Join Date: Apr 2020
Posts: 9
Received 0 Votes on 0 Posts
I was wondering if the two bars were bonded because I couldn't see and knew they should be.
 
  #10  
Old 01-06-21, 12:05 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,765
Received 97 Votes on 87 Posts
I was wondering if the two bars were bonded because I couldn't see and knew they should be.
But you said this was a subpanel. In a subpanel the neutral bus never gets bonded to the grounded panel box. The neutrals must be completely isolated from ground.
 
  #11  
Old 01-06-21, 04:54 PM
A
Member
Thread Starter
Join Date: Apr 2020
Posts: 9
Received 0 Votes on 0 Posts
The neutral bars should be bonded I know it should be separated from ground
 
  #12  
Old 01-06-21, 05:15 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,514
Received 125 Votes on 99 Posts
You are misusing the term bonded. In electrical, bonded refers to being connected to ground. As to the two neutral bars, they are interconnected but not bonded to ground.
 
  #13  
Old 01-06-21, 07:17 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,808
Received 253 Votes on 221 Posts
From the NEC book Art.100 Definitions:

Bonded (Bonding) Connected to establish electrical continuity and conductivity.

The two neutral bars can be bonded together, and not necessarily bonded to ground.

If this is a sub-panel where is the main disconnect?
 
 