Two 200 amp disconnect main

I have four green house and I want to pull a 100 amp to each greenhouse from the two 200 amp main service disconnect. What should I do? Should I just buy four 100 amp circuit breaker and run that to my subpanel?
 

Last edited by Audy Xiong; 02-16-21 at 03:44 PM.
  #2  
Old 02-16-21, 04:03 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
Should I just buy four 100 amp circuit breaker and run that to my subpanel?
Basically, yes. Run a separate 100 amp feeder to each greenhouse and install a sub-panel with a main breaker in each of them. You will need a 4 wire feeder using #3 copper and a ground rod at each location. If the greenhouse is steel you should also bond that.
 
  #3  
Old 02-16-21, 04:25 PM
A
Member
Thread Starter
Join Date: Feb 2021
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks! Do I need to bonding at the 2 main disconnect service if there are not bonding?
 
  #4  
Old 02-16-21, 05:28 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
Do I need to bonding at the 2 main disconnect service if there are not bonding?
Yes. There should at least one ground rod and some other grounding electrode (Ufer, Ground rod/pipe, water service, etc)
 
  #5  
Old 02-16-21, 06:23 PM
A
Member
Thread Starter
Join Date: Feb 2021
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
So I do have to connect neutrals and grounding/bonding for both of the main service panel or just one of the main panel.
 
  #6  
Old 02-17-21, 03:34 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
The neutrals of the main panels should terminate in their proper location in each panel. (one wire per panel)

Both main panels should be bonded together but can be connected to the grounding electrode using a single grounding electrode conductor.
 
 