Adding a subpanel questions
Old 03-05-21, 12:54 PM
Received 3 Votes on 3 Posts
I have been working on adding a subpanel, next to the main panel, in order to have electrical service in the basement, that I'm planning on finishing.
So far, everything seems straight forward. The neutral and ground wires are bonded in the main panel and isolated in the sub-panel. And I'm using 2-2-2-4 aluminum wire, between the two panels, for a 125A circuit.
My question is can I use aluminum wire for the ground wire between the panels? And should I add another grounding rod connected to the subpanel or let the ground piggyback off the main panel?
I apologize if this is a stupid question, I'm simply trying to meet code. Thanks in advance!
Old 03-05-21, 01:51 PM
Z
Received 190 Votes on 170 Posts
You're all set with your wiring layout. No need for another ground rod or extra ground wire as long as the subpanel is in the same building.
2ga AL will support a 100A feed. You can still use a larger subpanel, but the breaker in the main panel can be max 100A.
Old 03-05-21, 02:08 PM
P
Received 143 Votes on 116 Posts
#2 Al is good for up to 90A, not 100A when used for a branch feeder per the NEC.
Zorfdt voted this post useful.
Old 03-06-21, 04:41 AM
G
Received 1 Vote on 1 Post
How many amps do you need?
Old 03-06-21, 12:32 PM
CasualJoe's Avatar
Received 106 Votes on 94 Posts
You said you were using 2-2-2-4 aluminum wire, I assume it is 2-2-2-4 SER cable. If so, the #4 is your ground wire between the two panels.