Switch to recess lighting - help with Romex


  #1  
Old 04-14-21, 05:50 PM
C
Member
Thread Starter
Join Date: Sep 2016
Posts: 17
Received 0 Votes on 0 Posts
Switch to recess lighting - help with Romex

Hello all, I need some help. I want to switch from two down lights to four recessed lights. I took the main light down (L1 in image below) and was meet with the wiring you see on the right. The second down light is turned on by the same two switches (S2) as the primary light. However, I'm not sure where the wiring is coming from (I'm assuming L1). Can anyone tell me what they make of this wiring?:

 
  #2  
Old 04-14-21, 06:29 PM
L
Member
Join Date: Nov 2015
Posts: 1,612
Received 105 Votes on 91 Posts
The cable with only black and white wires is probably what runs to 2nd light. That is only cable connected in parallel with main light.

This is basically how your light is wired except that black and white wires coming from right switch is reversed.


To make things simple, you just have to connect wires exactly as is and connect new lights to black and white wires going to existing lights.

Unless you install recessed light in the exact place as old lights, you will either have to put blank cover and run wires from existing junction box or run new cable all the way to the switches.
 
  #3  
Old 04-15-21, 04:06 AM
C
Member
Thread Starter
Join Date: Sep 2016
Posts: 17
Received 0 Votes on 0 Posts
Thanks for the reply Lambition. I failed to mention, I'm doing away with the two current drop lights and replacing them with the recessed lighting in different locations. My plan was to drywall over the current boxes. I'll have to get in the attic to check, but I believe the light on the left (L2) just has wiring going in to it, not out of it. Can I just pull that wire out of the box and use it in the recessed lighting? I know I remove the pigtails coming down to the current light, but for the travelers in L1 do I just shove them up in the box and drywall over it? What's the best practices/codes to do drywall over a box (if there are any)?
 
  #4  
Old 04-15-21, 06:46 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,911
Received 326 Votes on 281 Posts
You can't drywall over the old boxes. They have to remain accessible. If they are in the attic you can turn them over and put a cover on them in the attic.
 
  #5  
Old 04-15-21, 05:43 PM
L
Member
Join Date: Nov 2015
Posts: 1,612
Received 105 Votes on 91 Posts
My plan was to drywall over the current boxes.
All splices must remain accessible. So, you cannot drywall over. You can turn box around to make it accessible form attic. But the catch is it should not be covered with insulation either. It is unlikely you will have enough slack to do so. You might have to run some new cable to bring junction box for splices above insulation.

Can I just pull that wire out of the box and use it in the recessed lighting?

Yes you can. But, since you have attic above, might as well as just run new cable from L1 and daisy chain from there.


What's the best practices/codes to do drywall over a box (if there are any)?
There are none. It should never be done.
 
  #6  
Old 04-16-21, 11:01 AM
C
Member
Thread Starter
Join Date: Sep 2016
Posts: 17
Received 0 Votes on 0 Posts
Okay, was able to get in the attic and take a peek. So the 12/3 and 12/2 from light 1 (L1) goes to light 2 (L2). I didn't have the time to track the 12/3 coming out of light 2. Here's a schematic of what it appears like from the top:



Here's what the lights look like from the top:







So can I just remove the current lights, pull the Romex out of the boxes, make up the Romex again in boxes facing up in the attic (boxes that have covers) and use the 12/2 from L1 and run it to power the four new recessed lights?
 
 