NEC restriction on an outlet near a water source???


  #1  
Old 04-28-21, 12:45 PM
S
Member
Thread Starter
Join Date: Jan 2005
Location: USA
Posts: 619
Received 0 Votes on 0 Posts
Exclamation NEC restriction on an outlet near a water source???

In my basement project, I want to place 120V and 24V receptacles in a spot that is also near [about 12"] from a water tap. It's where I need them.

The 120V circuit will be on a GFCI which fits the 6 foot rule. No easy way to do that for the 240V w/a GFCI receptacle that I know of. Is a GFCI circuit breaker doable to meet code? Is there another way and/or cheaper way?

Thanks guys!
 
  #2  
Old 04-28-21, 01:52 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: United States
Posts: 5,085
Received 96 Votes on 89 Posts
Hi, a 2 pole GFCI breaker would be fine.
Geo 🇺🇸
 
  #3  
Old 04-28-21, 06:23 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,208
Received 371 Votes on 321 Posts
Depending on your location, and what code cycle you are on, GFCI protection may not be required for a 240-volt receptacle. That requirement was added in the 2020 version of the NEC.
 
  #4  
Old 04-28-21, 08:08 PM
S
Member
Thread Starter
Join Date: Jan 2005
Location: USA
Posts: 619
Received 0 Votes on 0 Posts
Thanks guys!

Interesting point about the code cycle. When I submit the permit I'll ask.
 
  #5  
Old 04-29-21, 06:22 AM
I
Member
Join Date: Feb 2021
Posts: 111
Received 24 Votes on 19 Posts
I'd do the GFI breaker anyway, even if not required. Staying alive is worth a few bucks, ya know.
 
  #6  
Old 04-29-21, 12:55 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,612
Received 157 Votes on 129 Posts
I believe if the basement area is unfinished(basically bare concrete floor) NEC requires GFCI protection for receptacles.
 
  #7  
Old 04-30-21, 04:15 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,208
Received 371 Votes on 321 Posts
2020 NEC requires all receptacles located in a basement to be GFCI protected regardless if it is finished or not.
 
 