Wiremold and ungrounded circuits.
Old 06-10-21, 10:32 AM
Can someone verify that NEC 250.86 allows the use of raceway like Wiremold to extend ungrounded circuits up to 25 feet? That what is seems to say. Thanks for your help.
Neil
Popular Reply
06-10-21, 02:26 PM
joed
joed is offline
Received 336 Votes on 289 Posts
As far as I know ungrounded circuits are not permitted to be extended by any method.
Old 06-10-21, 02:26 PM
CasualJoe, Spielbass voted this post useful.
Old 06-10-21, 04:48 PM
Tolyn Ironhand's Avatar
Received 365 Votes on 316 Posts
You are not allowed to extend an ungrounded circuit.
205.86 exception #1 is only for protecting existing installations.
Old 06-11-21, 12:49 AM
What would an existing installation be? Protecting exposed wiring?
Old 06-11-21, 06:09 PM
L
Received 16 Votes on 12 Posts
Whether or not the wiremold needs to be grounded, you still have to comply with 250.130(c): must run a ground wire for the new outlets. Which probably isn't less work than running a new circuit.
Old Yesterday, 07:03 AM
Protecting wiring that was installed under an earlier code cycle.