Proper switches and outlets for a 20 amp ciruit

Reply

  #1  
Old 06-25-01, 07:34 AM
Member
Thread Starter
Join Date: Jun 2001
Location: Pennsylvania
Posts: 240
I wish to run a 20 amp circuit to a bathroom. The most common switches and outlets I've seen in stores have 15A imprinted on them. Can these be used, or do I need hardware specific for a 20 amp circuit? Thanks in advance.
 
Sponsored Links
  #2  
Old 06-25-01, 07:45 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
This is a very frequently asked question.

The answer is that code does allow you to use the 15-amp receptacles and switches on a 20-amp circuit. There is only one tiny exceptions which requires a 20-amp receptacle if that is the only receptacle on the whole circuit (and duplex receptacles count as two).

Some have said that a quality 15-amp receptacle and a 20-amp receptacle are manufactured to the same specifications anyway, and the only difference is the shape of the slots in the faceplate. If this is true, then a 20-amp receptacle isn't even any better than a 15-amp receptacle.
 