dryer and water heater wiring

Reply

  #1  
Old 06-26-01, 06:27 PM
Visiting Guest
Posts: n/a
In my utility shed I have a 40 gallon hot water heater that has 10-2 wiring running thru a 30 amp fuse box. I also have an electric dryer that has a seperate circuit running off the main. It is 240 but I dont know what size wire it is. Can I run the water heater off the same cicuit the dryer is running on? What size wire and circuit breakers do I need for these two item? Any help would be appreciated. ..email.... [email protected]
 
Sponsored Links
  #2  
Old 06-26-01, 07:23 PM
s1nuber
Visiting Guest
Posts: n/a
You cannot install a water heater and a clothes dryer on the same circuit and be code compliant. Most residential electric water heaters need a 30 amp 240 volt circuit (10/2 w/gnd is fine).

Most residential clothes dryers also need a 30 amp 240 volt circuit, but a new dryer needs a 10/3 w/gnd (or 4 wire) circuit.

If this is in a utility shed, does this mean that the shed is detached from the main house? This would open up a whole different can of worms. In general, 30 amp circuits and 10 gauge wire for both units. 3 wire is ok for the water heater, 4 wire needed for the dryer. Post back if you have any further questions.

Enjoy your day!
 
  #3  
Old 06-27-01, 03:49 AM
Visiting Guest
Posts: n/a
still confused

thank you very much for your reply. the shed is actually a carport attached to the house and fully enclosed with full walls. could I install a sub-panel with breakers for the seperate circuits. 2 30 amp circuits, one for the water heater and one for the dryer, plus a couple of 20 amp circuits for my window air conditioner, lighting and outlets? what size cooper wire would I need to run to the sub-panel? how many amp would the main breaker need to be? thanks again for your help........michael
 
  #4  
Old 06-27-01, 03:53 AM
Visiting Guest
Posts: n/a
funny noises

I live in a mobile home and everytime I pull the chain on my ceiling fan in the bedroom to increase or decrease its speed I hear a loud noise through my stereo speakers in the living room. any suggestions has to whats going on and how to eliminate this?
 
  #5  
Old 06-27-01, 12:15 PM
Visiting Guest
Posts: n/a
I would apply a demand-factor of 100% to the Dryer& WH & AC load which would be approx. a 50 amp feeder current.I advise a #4 feeder cable on a 100amp CB. What is the rating of the Main CB at the service and the # of breakers the service panel is sized for? Any spare spaces?
 
  #6  
Old 06-27-01, 05:25 PM
Visiting Guest
Posts: n/a
thanks switchman

#4 wire to 100 amp box, sounds good. then I need 2 seperate 50 amp breakers, one for the dryer and one for the water heater, with maybe 10 ga wire? I haven't crawled under the trailer far enough to see what amp service is there but it is a huge panel and lots of extra space for more breakers. thanks so much for your reply.....Michael
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: