12/2 romex on 15A breaker?

I need to relocate the 14/2 romex going to my dishwasher. It's a 15A dedicated circuit per manufacturer. When I reroute it, it isn't long enough. I have a lot of 12/2 romex, but no 14/2. Can I run my 12/2 from the 15A breaker, to the dishwasher?
 
  #2  
Old 01-06-22, 09:58 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 5,004
Likes: 0
Received 244 Likes on 224 Posts
Yes, not a problem.

Yes, it is overkill, but you save time otherwise spent brainstorming, shopping online, and making the trip to the store to buy 14 gauge cable.
 
  #3  
Old 01-06-22, 10:02 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 28,567
Received 1,702 Likes on 1,521 Posts
Yes, using a larger wire size is permitted.
 
  #4  
Old 01-06-22, 10:07 AM
B
Member
Thread Starter
Join Date: Oct 2001
Location: USA
Posts: 997
Received 8 Likes on 8 Posts
Thanks for the responses!
 
  #5  
Old 01-06-22, 07:20 PM
Join Date: Jan 2009
Location: United States
Posts: 1,089
Received 73 Likes on 68 Posts
Not required but I would still put a mark somewhere on the panel/breaker legend that says 15A Max 14AWG is installed somewhere in the circuit or some wording I'm sure can be expressed easier then mine LoL!
 
The following users liked this post:
  #6  
Old 01-07-22, 12:30 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 11,206
Received 172 Likes on 155 Posts
Can I run my 12/2 from the 15A breaker, to the dishwasher?
Yes, you can. I'd also change the breaker to 20 amps.
 
  #7  
Old 01-07-22, 02:59 PM
Join Date: Jan 2009
Location: United States
Posts: 1,089
Received 73 Likes on 68 Posts
Yes, you can. I'd also change the breaker to 20 amps.
Only if the entire run is 12AWG though.
 
The following users liked this post:
  #8  
Old 01-08-22, 02:28 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 11,206
Received 172 Likes on 155 Posts
Only if the entire run is 12AWG though.
The question was
​​​​​​​ Can I run my 12/2 from the 15A breaker, to the dishwasher?
That means to me a new dedicated circuit of 12-2. No mention of any 14-2 at all.
 
  #9  
Old 01-08-22, 07:04 PM
Join Date: Jan 2009
Location: United States
Posts: 1,089
Received 73 Likes on 68 Posts
Um
I need to relocate the 14/2 romex
 
  #10  
Old 01-11-22, 07:54 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 11,206
Received 172 Likes on 155 Posts
I need to relocate the 14/2 romex
But rather than relocate the 14-2 the alternate the OP asked about was.
​​​​​​​ I have a lot of 12/2 romex, but no 14/2. Can I run my 12/2 from the 15A breaker, to the dishwasher?
No mention of using any 14-2 in the new dedicated circuit. I still recommend using a 20 amp breaker.
 