Running power from garage to shed


  #1  
Old 08-10-22, 03:10 PM
M
Member
Thread Starter
Join Date: May 2006
Posts: 76
Received 0 Votes on 0 Posts
Running power from garage to shed

I am running a 20 Amp dedicated circuit to the shed in rigid conduit 6+" deep. I have a weatherproof mounted to the LB conduit body outside of the garage.

I ran 12ga THWN wires from the shed to the LB conduit body Can indoor Romex be in the LB conduit body on the outside of the garage Or what are my options? I am going to use romex from the panel in the garage.

Thanks
 
  #2  
Old 08-10-22, 03:17 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 70,108
Received 2,957 Votes on 2,668 Posts
You can use NM-b from the LB to inside.
There cannot be any NM-b used outside.... in conduit or not in conduit.

Best to run separate conductors but if you want to run a cable.... use #12 UF.
 
  #3  
Old 08-10-22, 07:44 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,964
Received 595 Votes on 511 Posts
LBs are quite small and only some are allowed to splice in. I would recommend using an outdoor-rated metal box instead of an LB. Another option is to run an RMC nipple into the building and connect it to a 4x4" steel box. You are also required to bond the ground to the steel conduit if it is not run continuously between pull points.
 
  #4  
Old 08-11-22, 02:30 AM
Marq1's Avatar
Member
Join Date: Sep 2016
Location: USA MI
Posts: 9,490
Received 950 Votes on 862 Posts
rigid conduit 6+" deep
Isn't the requirement for buried conduit 18" deep?
 
  #5  
Old 08-11-22, 07:50 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,850
Received 210 Votes on 178 Posts
RMC can be 6".
 
 