Need some expertise with a breaker box

When I check each leg of my water heater breaker they each read 120 respectively. When I measure them together they only read 26. I also get the same reading of 26 together at the main breaker in the sub panel. And that's as far back to the meter box as I've gone so far. Any help is greatly appreciated.
 
  #2  
Old 11-25-22, 04:45 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,372
Received 475 Upvotes on 391 Posts
One of the hot legs is dead. Check the breaker feeding the sub panel. Turn it off and back on to make sure it is reset on both sides.
 
  #3  
Old 11-25-22, 08:16 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,415
Received 163 Upvotes on 142 Posts
Do other large 240 volt appliances work properly? You may need to call the power company.
 
  #4  
Old 11-26-22, 03:13 AM
A
Member
Join Date: Mar 2014
Posts: 891
Received 124 Upvotes on 104 Posts
If the water heater is being fed from the sub panel and that is the breaker you tested as you reported did you check the breaker feeding the sub panel?

 
 