100A Garage Loft Sub Panel Questions
New construction garage with loft, sub-panel to be ~25ft from the garage level main panel. I probably don't need 100A but prefer at least 6 circuits and haven't found a Homeline that would work other then the one noted below.
Square D Homeline 100-Amp 8-Space sub-panel in loft of new detached garage. The sub-panel will be fed by the existing 200A panel in garage which has its own separate service/meter (not from house). Ive read that 100A sub requires #4 copper or #2 aluminum. I cant seem to locate #4 copper or Al in SER sheath local but I can get Southwire-2-2-2-4-Black-Stranded-Al-MHF by the foot.
Can I run the 2-2-2-4 shown from the main through drilled holes in the sill/joists/studs like a typical run or will it require conduit?
Any other suggestions is appreciated.
Thanks. FF
Square D Homeline 100-Amp 8-Space sub-panel in loft of new detached garage. The sub-panel will be fed by the existing 200A panel in garage which has its own separate service/meter (not from house). Ive read that 100A sub requires #4 copper or #2 aluminum. I cant seem to locate #4 copper or Al in SER sheath local but I can get Southwire-2-2-2-4-Black-Stranded-Al-MHF by the foot.
Can I run the 2-2-2-4 shown from the main through drilled holes in the sill/joists/studs like a typical run or will it require conduit?
Any other suggestions is appreciated.
Thanks. FF
Last edited by FairwayFatty; 11-28-22 at 09:11 AM.
#2
100A sub requires 4/0 copper or 2/0 aluminum.
4/0 is +200 amps.
FairwayFatty
voted this post useful.
#3
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,704
Received 273 Upvotes
on
230 Posts
FairwayFatty
voted this post useful.
#4
Member
Thread Starter
Could I use #2 Copper (By-the-Foot) 2 Black Stranded CU SIMpull THHN Wire
If so:
Would 2 black, 1 white and 1 green (what size green would be needed?
They dont have #2 green would #6 green be sufficient for the ground?
If so:
Would 2 black, 1 white and 1 green (what size green would be needed?
They dont have #2 green would #6 green be sufficient for the ground?
#5
Member
Are you after 100A for the subpanel due to the future expected loads? Or just trying to size a panel with enough spaces?
If you are just after a decent quantity of single pole spaces, you can use pretty much anything for a subpanel. You could even put in a 200A main 42 space panel if you want, and feed it with a 40A feed. I just don't want you to think that just because the label on the box says 100A that you MUST feed it at that rating. The breaker in the main panel feeding the sub is what will drive the conductor size to use.
If you are just after a decent quantity of single pole spaces, you can use pretty much anything for a subpanel. You could even put in a 200A main 42 space panel if you want, and feed it with a 40A feed. I just don't want you to think that just because the label on the box says 100A that you MUST feed it at that rating. The breaker in the main panel feeding the sub is what will drive the conductor size to use.
CasualJoe,
FairwayFatty
voted this post useful.
#6
Forum Topic Moderator
I agree with Caddymac's statement. What are your anticipated loads in the loft? If it's just a bathroom plus some receptacles/lights, you can get by with a 30A feed. If you're running a water heater, heater/AC, then you're probably looking at a 60A feed.
100A is a lot of power and probably not required for your loft space. As mentioned, it's definitely worth getting a 100A panel for the breaker spaces, but then feeding it with 30/40/60A cable and breaker in your main panel as needed.
100A is a lot of power and probably not required for your loft space. As mentioned, it's definitely worth getting a 100A panel for the breaker spaces, but then feeding it with 30/40/60A cable and breaker in your main panel as needed.
FairwayFatty
voted this post useful.
#7
Member
Thread Starter
Are you after 100A for the sub-panel due to the future expected loads? Or just trying to size a panel with enough spaces?
50A apartment size stove/oven
20A microwave
20A refrigerator
20A entertainment center
15A bath and outlets
15A general lighting
15A general outlets
Thanks for the response and any suggestions.
#8
The 100 amp panel can be fed with up to a 100 amp feeder. It can be smaller. Aluminum cable will be much more economical to run than copper.
THHN is for use in conduit. It cannot be run in free air or through the studs.
Bathroom receptacles should be on 20 amp circuits.
With your list above you have maxxed out the number of spaces, 8.
THHN is for use in conduit. It cannot be run in free air or through the studs.
Bathroom receptacles should be on 20 amp circuits.
With your list above you have maxxed out the number of spaces, 8.
CasualJoe,
FairwayFatty
voted this post useful.
#9
Member
Thread Starter
Does the attached load calculation of 59A look reasonable (large loft room with small bath) and would I need to go with an 80A (59*1.25=73.75) breaker and ok to use 4-4-4-6 copper on 20ft run? Larger SER wire seems to be hard to get local.
(Pending mini split fed by 200A in garage level not loft panel)
(Pending mini split fed by 200A in garage level not loft panel)
#10
You typically will not find larger cables with copper conductors. Aluminum will be 1/3 of the cost of copper, be easier to work with and weigh less.