Can a 240V water heater be converted to 120V?
#1
Can a 240V water heater be converted to 120V?
I bought a new 12 gallon water heater off Craigslist a while back. Before doing so I looked up the specs and saw it was 120V which is what I needed, so I bought it. Now, months later, I am ready to install it and find it is actually a 240V water heater.
What are my options? I want it to be safe and meet code. Can I run this on 120V as is? Can I install a 120V element? Or should I just resell it and move on to the appropriate 120V model?
What are my options? I want it to be safe and meet code. Can I run this on 120V as is? Can I install a 120V element? Or should I just resell it and move on to the appropriate 120V model?
#2
How many watts is the element? What is the intended purpose? Twelve gallons sounds like for a small bathroom sink and nothing else. Do you have a dedicated circuit for this?
#3
The element is 1500W. This will only be used to heat water for a utility sink in the garage. I do not have a dedicated circuit for this.
#4
Member
Halving the voltage will half the wattage the element can produce. This will increase the time to heat the water to any temperature. Only you know the time and temperature that is acceptable for your purposes. Operating a 1500 watt element at 120 vac draws 12.5 amps. This leaves little room for other loads on a 15 amps circuit without tripping breaker.
#5
Are you saying I could wire is up as if it were 120V? Black to black, white to red? Recovery time is not a big deal to me. I will use it to wash my hands periodically. The circuit is not dedicated, but is a circuit used by little or nothing else.
Based on what I reading, I can use the water heater as-is, but recovery time will be slow. And I run the risk of tripping a circuit breaker if trying to use other outlets on the same circuit? Correct?
The thing is, I already own this and cannot return it. My options are use it or try to sell it and get something else.
Based on what I reading, I can use the water heater as-is, but recovery time will be slow. And I run the risk of tripping a circuit breaker if trying to use other outlets on the same circuit? Correct?
The thing is, I already own this and cannot return it. My options are use it or try to sell it and get something else.
#6
Member
My error. Halving the voltage will result in element producing one quarter the wattage since current is also halved because element resistance is constant. Suggest running a 240 vac circuit to the garage.
#7
Member
Increasing the recovery time by 4 could make your water heater a continuous load. Plus, a breaker should not be loaded to more than 80% of its rated value. Unless this is a 20 amp circuit (#12 conductors fed from a 20 amp breaker), I would not recommend doing what you suggest. At a minimum it's inadvisable and could be dangerous. I hope a pro will be along to explain it better.
#8
At 240 volts the element draws 6 (6.25) amps to provide 1.5 kilowatts of heat. At 120 volts the same element will draw fewer amps (roughly 3, producing roughly 0.4 KW of heat) so there is no problem with continuous versus intermittent load calculations. Go ahead and hook the heater up to a 120 volt circuit if you want to, temporarily.
Last edited by AllanJ; 12-07-22 at 06:41 AM.
SJMaye
voted this post useful.
#9
Member
You can simply just connect it to 120 volts and it will work. It will take longer to heat up but it will work. I have a 40 gallon unit that has been running this way for 10 years at my cottage.
SJMaye
voted this post useful.
#10
Thanks, AllanJ. I did not want to do anything questionable or, especially, unsafe. It sounds like the recovery thing is more of an inconvenience if anything.
#11
Oh, by the way, at 120 volts, according to my calculations, the water inside will still reach the maximum recommended temperature of 120 degrees F.
SJMaye
voted this post useful.
#12
It doesn't matter the size of the element or wattage. If no water is used it will reach maximum temperature..... eventually. One good thing.... a 240v element running on 120v will probably never burn out.
On the other hand... you could probably replace the 240v element with a 120v element.
On the other hand... you could probably replace the 240v element with a 120v element.
SJMaye
voted this post useful.
#13
On the other hand... you could probably replace the 240v element with a 120v element
SJMaye
voted this post useful.
#15
Half voltage will result in approx 1/4 wattage. 1500/4=375W
That will result in loooong time to heat it up, but only use approx 1.2 Ampere.
You can not rouin anything by testing. It will probably need to run to the next day to be hot.
That will result in loooong time to heat it up, but only use approx 1.2 Ampere.
You can not rouin anything by testing. It will probably need to run to the next day to be hot.
SJMaye
voted this post useful.
#17
The same rules apply as for gas water heaters: Shut off the power-- both the breaker and the required shutoff switch near the tank.-- before draining the tank. See water gushing from a hot faucet for a minute before turning the breaker back on.
One hundred twenty volts into the 240 volt element without water in the tank can still burn it out.very quickly.
One hundred twenty volts into the 240 volt element without water in the tank can still burn it out.very quickly.
#18
The replacement elements are cheap. Since it is a new install I may just install the correct 120V element now. Is the element the only real difference between a 240V and 120V electric water heater.
#19
Member
If your water heater is on dedicated circuit (and it should be) then it is better to rewire the circuit to 240V. Just replace with 2 pole breaker matching wire size and move white wire from neutral to one of the poles on the breaker.
#20
You will have a choice of element wattages. If you choose a 1500 watt 120 volt element then go back to the posts above (I think #4 and #7) regarding continuous versus intermittent load. You may well need to upgrade the wiring and, if you need to string a new circuit you might as well do it as a 240 volt circuit.
Fifteen hundred watt space heaters are sold everywhere for use on 15 amp circuits
Fifteen hundred watt space heaters are sold everywhere for use on 15 amp circuits
SJMaye
voted this post useful.
#21
If you choose a 1500 watt 120 volt element then go back to the posts above (I think #4 and #7) regarding continuous versus intermittent load. You may well need to upgrade the wiring
#22
Yet a (theoretical here) 1500 watt 120 volt water heater violates the intermittent/continuous rule on a 15 amp circuit (it needs 15-1/2 amp circuit, round that up to 20 amp circuit to comply). But you have to draw the line somewhere and the NEC code book uses 80% of the circuit and breaker amps rating as the maximum for continuous loading, (Or a 125% fudge factor to, given the actual loading, figure out the needed circuit amps rating) It is too complicated for me to describe here a variety of circuit wattages and element wattages to match different permutations of goals and objectives.
Last edited by AllanJ; 12-08-22 at 05:56 AM.
SJMaye
voted this post useful.
#23
Pretty much universal. Either bolt in or screw in.
#24
A lot of discussion over circuit size. I don't believe the OP has ever mentioned circuit size here.
My point was there are two styles of element in use.... it's either A or B.
My point was there are two styles of element in use.... it's either A or B.
SJMaye
voted this post useful.