Can a 240V water heater be converted to 120V?

I bought a new 12 gallon water heater off Craigslist a while back. Before doing so I looked up the specs and saw it was 120V which is what I needed, so I bought it. Now, months later, I am ready to install it and find it is actually a 240V water heater.

What are my options? I want it to be safe and meet code. Can I run this on 120V as is? Can I install a 120V element? Or should I just resell it and move on to the appropriate 120V model?
 
  #2  
Old 12-07-22, 02:42 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,977
Received 194 Upvotes on 170 Posts
How many watts is the element? What is the intended purpose? Twelve gallons sounds like for a small bathroom sink and nothing else. Do you have a dedicated circuit for this?
 
  #3  
Old 12-07-22, 02:44 AM
SJMaye's Avatar
Member
Thread Starter
Join Date: Feb 2011
Location: United States
Posts: 291
Received 1 Upvote on 1 Post
The element is 1500W. This will only be used to heat water for a utility sink in the garage. I do not have a dedicated circuit for this.
 
  #4  
Old 12-07-22, 04:10 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 3,201
Received 292 Upvotes on 259 Posts
Halving the voltage will half the wattage the element can produce. This will increase the time to heat the water to any temperature. Only you know the time and temperature that is acceptable for your purposes. Operating a 1500 watt element at 120 vac draws 12.5 amps. This leaves little room for other loads on a 15 amps circuit without tripping breaker.
 
  #5  
Old 12-07-22, 04:19 AM
SJMaye's Avatar
Member
Thread Starter
Join Date: Feb 2011
Location: United States
Posts: 291
Received 1 Upvote on 1 Post
Are you saying I could wire is up as if it were 120V? Black to black, white to red? Recovery time is not a big deal to me. I will use it to wash my hands periodically. The circuit is not dedicated, but is a circuit used by little or nothing else.

Based on what I reading, I can use the water heater as-is, but recovery time will be slow. And I run the risk of tripping a circuit breaker if trying to use other outlets on the same circuit? Correct?

The thing is, I already own this and cannot return it. My options are use it or try to sell it and get something else.
 
  #6  
Old 12-07-22, 05:24 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 3,201
Received 292 Upvotes on 259 Posts
My error. Halving the voltage will result in element producing one quarter the wattage since current is also halved because element resistance is constant. Suggest running a 240 vac circuit to the garage.
 
  #7  
Old 12-07-22, 05:41 AM
T
Member
Join Date: Sep 2015
Location: US
Posts: 1,182
Received 195 Upvotes on 171 Posts
Increasing the recovery time by 4 could make your water heater a continuous load. Plus, a breaker should not be loaded to more than 80% of its rated value. ​​​​​​​Unless this is a 20 amp circuit (#12 conductors fed from a 20 amp breaker), I would not recommend doing what you suggest. At a minimum it's inadvisable and could be dangerous. ​​​​​​​ I hope a pro will be along to explain it better.​​​​​​​​​​​​​​
 
  #8  
Old 12-07-22, 06:24 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,515
Upvotes: 0
Received 276 Upvotes on 252 Posts
At 240 volts the element draws 6 (6.25) amps to provide 1.5 kilowatts of heat. At 120 volts the same element will draw fewer amps (roughly 3, producing roughly 0.4 KW of heat) so there is no problem with continuous versus intermittent load calculations. Go ahead and hook the heater up to a 120 volt circuit if you want to, temporarily.
 

Last edited by AllanJ; 12-07-22 at 06:41 AM.
SJMaye voted this post useful.
  #9  
Old 12-07-22, 06:30 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,036
Received 515 Upvotes on 420 Posts
You can simply just connect it to 120 volts and it will work. It will take longer to heat up but it will work. I have a 40 gallon unit that has been running this way for 10 years at my cottage.
 
SJMaye voted this post useful.
  #10  
Old 12-07-22, 06:31 AM
SJMaye's Avatar
Member
Thread Starter
Join Date: Feb 2011
Location: United States
Posts: 291
Received 1 Upvote on 1 Post
Thanks, AllanJ. I did not want to do anything questionable or, especially, unsafe. It sounds like the recovery thing is more of an inconvenience if anything.
 
  #11  
Old 12-07-22, 06:53 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,515
Upvotes: 0
Received 276 Upvotes on 252 Posts
Oh, by the way, at 120 volts, according to my calculations, the water inside will still reach the maximum recommended temperature of 120 degrees F.
 
SJMaye voted this post useful.
  #12  
Old 12-07-22, 09:47 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,811
Received 3,922 Upvotes on 3,518 Posts
It doesn't matter the size of the element or wattage. If no water is used it will reach maximum temperature..... eventually. One good thing.... a 240v element running on 120v will probably never burn out.

On the other hand... you could probably replace the 240v element with a 120v element.
 
SJMaye voted this post useful.
  #13  
Old 12-07-22, 10:00 AM
SJMaye's Avatar
Member
Thread Starter
Join Date: Feb 2011
Location: United States
Posts: 291
Received 1 Upvote on 1 Post
On the other hand... you could probably replace the 240v element with a 120v element
I don't think I will notice the slow recovery time as little as I will use this, but if I do I will try replacing the element as you suggest. Are these universal or would I have to buy one for this model and manufacturer?
 
  #14  
Old 12-07-22, 10:13 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,811
Received 3,922 Upvotes on 3,518 Posts
Pretty much universal. Either bolt in or screw in.
 
SJMaye voted this post useful.
  #15  
Old 12-07-22, 12:45 PM
d_s_k's Avatar
Member
Join Date: Mar 2007
Location: Norway
Posts: 406
Received 22 Upvotes on 20 Posts
Half voltage will result in approx 1/4 wattage. 1500/4=375W
That will result in loooong time to heat it up, but only use approx 1.2 Ampere.
You can not rouin anything by testing. It will probably need to run to the next day to be hot.

 
SJMaye voted this post useful.
  #16  
Old 12-07-22, 04:39 PM
Join Date: Jan 2009
Location: United States
Posts: 1,041
Received 78 Upvotes on 73 Posts
Just make sure the tank has water in it before hooking up power! or you risk burning out you element
 
d_s_k, SJMaye voted this post useful.
  #17  
Old 12-07-22, 06:09 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,515
Upvotes: 0
Received 276 Upvotes on 252 Posts
The same rules apply as for gas water heaters: Shut off the power-- both the breaker and the required shutoff switch near the tank.-- before draining the tank. See water gushing from a hot faucet for a minute before turning the breaker back on.

One hundred twenty volts into the 240 volt element without water in the tank can still burn it out.very quickly.
 
d_s_k, SJMaye voted this post useful.
  #18  
Old 12-08-22, 01:06 AM
SJMaye's Avatar
Member
Thread Starter
Join Date: Feb 2011
Location: United States
Posts: 291
Received 1 Upvote on 1 Post
The replacement elements are cheap. Since it is a new install I may just install the correct 120V element now. Is the element the only real difference between a 240V and 120V electric water heater.
 
  #19  
Old 12-08-22, 04:47 AM
L
Member
Join Date: Nov 2015
Posts: 1,572
Received 201 Upvotes on 172 Posts
If your water heater is on dedicated circuit (and it should be) then it is better to rewire the circuit to 240V. Just replace with 2 pole breaker matching wire size and move white wire from neutral to one of the poles on the breaker.
 
  #20  
Old 12-08-22, 05:24 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,515
Upvotes: 0
Received 276 Upvotes on 252 Posts
You will have a choice of element wattages. If you choose a 1500 watt 120 volt element then go back to the posts above (I think #4 and #7) regarding continuous versus intermittent load. You may well need to upgrade the wiring and, if you need to string a new circuit you might as well do it as a 240 volt circuit.

Fifteen hundred watt space heaters are sold everywhere for use on 15 amp circuits

 
SJMaye voted this post useful.
  #21  
Old 12-08-22, 05:28 AM
SJMaye's Avatar
Member
Thread Starter
Join Date: Feb 2011
Location: United States
Posts: 291
Received 1 Upvote on 1 Post
If you choose a 1500 watt 120 volt element then go back to the posts above (I think #4 and #7) regarding continuous versus intermittent load. You may well need to upgrade the wiring
Good point. To be honest, at this point in my garage build I have no interest in running a new circuit. Reasons I won't boar anyone with. Based on that, I will likely stick with the current element. Like I said, this will be used for washing my hands when I happen to be working in the garage. Recovery time will not be an issue.
 
  #22  
Old 12-08-22, 05:31 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,515
Upvotes: 0
Received 276 Upvotes on 252 Posts
Yet a (theoretical here) 1500 watt 120 volt water heater violates the intermittent/continuous rule on a 15 amp circuit (it needs 15-1/2 amp circuit, round that up to 20 amp circuit to comply). But you have to draw the line somewhere and the NEC code book uses 80% of the circuit and breaker amps rating as the maximum for continuous loading, (Or a 125% fudge factor to, given the actual loading, figure out the needed circuit amps rating) It is too complicated for me to describe here a variety of circuit wattages and element wattages to match different permutations of goals and objectives.
 

Last edited by AllanJ; 12-08-22 at 05:56 AM.
SJMaye voted this post useful.
  #23  
Old 12-09-22, 03:40 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
Pretty much universal. Either bolt in or screw in.
I used to prefer the bolt-in elements, but haven't seen a water heater with bolt-in elements in years. I can't remember the last time I saw a replacement bolt-in element either.
 
  #24  
Old 12-09-22, 03:52 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,811
Received 3,922 Upvotes on 3,518 Posts
A lot of discussion over circuit size. I don't believe the OP has ever mentioned circuit size here.
My point was there are two styles of element in use.... it's either A or B.
 
SJMaye voted this post useful.
 