WIring Help, 2 circuits wired together red to black
Hello everyone. thanks for reading this.
I am trying to install a timer for my porch lights and a dimmer switch for my foyer chandelier. Both are fairly straightforward but when I opened my multi-gang box I could not get all the power off. I opened the circuit for the foyer and that dropped the current from 122V to 49V. I realized that there is a black from the living room circuit connected to the red from the foyer circuit. When I open the living room circuit everything goes to <0.2V.
Why would the black from one breaker be connected to the red of another breaker?
All the neutrals from both circuits are also wired together.
How would I correct this?
Thanks again to anyone taking the time.
Wiring for porch and chandelier switch with the black and red of different circuits connected Wiring schematic for porch and chandelier switch with the black and red of different circuits connected
breaker panel
Reason: added image
Two circuits sharing a neutral would be a MWBC (multiwire branch circuit). Google it for a full explanation of how they are formed and what they are used for.
B#1 seems to be the MWBC. It should be a two pole breaker or two single pole breakers one on top of the other tied together with a pin at the handles.
Are you sure B#2 is a breaker?. Would seem it is just feeding another cable.
The two switches are being fed by B#!.
3 way chand and single pole porch (no such thing as a 2 way).
I would double check to see if cable #2 is connected to a breaker.
If #2 is a breaker it should not be connected to neutral or hot from B#1. B#1 if is a MWBc is sharing its neutral from the 2 pole breaker it is connected to which is fine but should not be connected to the neutral of B#2 which could overload the neutral.
If B#2 is a breaker I would disconnect the red and black and wire nut them separately and disconnect the white neutrals. Wire nut the white neutrals as B#1 whites together and cap off the white neutral from B#2.
It's still early in the morning for me and I am running on 1/2 cup of coffee but if B#2 is a breaker I don't see why it would be connected to B#1 which should be a two pole breaker. It would seem that what you show as B#2 is a feed from B#1 going somewhere else and not power coming into the box from B#2.
Someone else please double check me here.
If the red from B#1 and the black from B#2 (that is if B#2 is a breaker) and they are on opposite legs then black and red will give you two hots of 240v
Something just is not right here.
It also looks as though someone used two tandems to create mWBCs. No tie bars and also not the right way to do it. A MWBC should be to a two pole or two single poles connected together with a tie bar.
How did you determine the connected black and red come from two different breakers? I think you have misidentified the wiring. The 49v reading you are seeing could be phantom voltage and is also confusing things for you. I assume you are using a digital multimeter.
It's not how the mwbc is used. It is two distinct circuits sharing a common neutral.
The problem is when only one breaker gets opened and then the neutral is worked on.
Once the neutral opens the second circuit feeds back thru the first circuit.
Code has demanded that either a 2P breaker be used or 2) single pole breakers with a handle tie.
It is desirable to have both circuits disconnected when either one is being worked on.
For the discussion... it would be helpful to know how the panel is labeled.
If we assume every handle has its own number.... odds on the left.... 4th and 5th handles down.
#7 is red
#9 is black
Two tandem breakers.... no handles tied.
The panel has mostly MWBC's and no tie handles. That shouldn't have passed inspection.
That means the breaker 1 cable is the feed. (two circuits)
#7 red feeds power to what's labeled breaker 2.
#9 black feeds the lights.
Apologies pattenpAFJES I did not do my part and test fully.
The final verdict is as stated in #4 above "That means the breaker 1 cable is the feed. (two circuits) #7 red feeds power to what's labeled breaker 2. #9 black feeds the lights."
Diagram showing two circuits in one feed using a common neutral with red connected to black
This would mean that the 49v I detected originally along the "foyer" circuit 1 (above), after opening that breaker, was indeed "ghost current" as others have suggested from the closed circuit 2 "living" that was alongside.
Is the a code violation? It looks like a MWBC that uses a 3-wire to 2-wire.
The requirements for a simultaneous disconnect came about after your house was built. Previously it was only required if both hots landed on the same yoke.
I bought a new 12 gallon water heater off Craigslist a while back. Before doing so I looked up the specs and saw it was 120V which is what I needed, so I bought it. Now, months later, I am ready to install it and find it is actually a 240V water heater.
What are my options? I want it to be safe and meet code. Can I run this on 120V as is? Can I install a 120V element? Or should I just resell it and move on to the appropriate 120V model?
Is it acceptable to route [url=https://www.lowes.com/pd/8-3-UF-Wire-By-the-Foot/3129381]8 / 3 Stranded UF[/url] in lieu of [url=https://www.lowes.com/pd/Southwire-Romex-SIMpull-8-3-Indoor-Non-Metallic-Jacket-Wire-By-the-Foot/50101580]8 / 3 Stranded Indoor Non-Metallic Wire[/url] through studs and joists and across attic then down through the wall to a 20" 220V 40A electric range?
The space is not accessible by permanent stairs or ladders, and will be protected within 6 ft of the access scuttle.
The total run is ~60 feet and he UF is $3 per foot and the NM is $6.25
Price and availability of wire is crazy around here.
Thanks for any advice.