Limits of a 20 Amp Circuit
#1
Member
Thread Starter
Limits of a 20 Amp Circuit
We have a property soon to be occupied after a so-so remodel. Checking it out, I noticed there are 5 outlets on the kitchen counter. (Protected by one GFCI) So I got curious and found out they were all on one 20 amp breaker. Looking further that 20 amp breaker also supplies 2 outlets in the master bathroom and 3 outlets in the dining room.
Would the norm be 3 maybe 4 separate circuits to carry all this?
Meanwhile I'm trying to understand the limits of a 20 amp circuit. 1st I understand that's 2,400 watts max. Secondly, however that breakers don't really trip until they hit about 130% of that value? Is that accurate? (That would be 3,120 Watts) Or something like that....? Does a 20 amp breaker trip at exactly 20 amps?
Going forward, We're trying to consider all the factors involved. And if the worst thing is simply nuisance tripping? Since we may or may not rectify all this prior to the place being occupied.
Would the norm be 3 maybe 4 separate circuits to carry all this?
Meanwhile I'm trying to understand the limits of a 20 amp circuit. 1st I understand that's 2,400 watts max. Secondly, however that breakers don't really trip until they hit about 130% of that value? Is that accurate? (That would be 3,120 Watts) Or something like that....? Does a 20 amp breaker trip at exactly 20 amps?
Going forward, We're trying to consider all the factors involved. And if the worst thing is simply nuisance tripping? Since we may or may not rectify all this prior to the place being occupied.
#2
By code.... there should be 2) 20A dedicated "counter only" receptacle circuits.
You can put several counter receptacles on each circuit.
One 20A circuit is going to be limited if you use several appliances at once.
You can put several counter receptacles on each circuit.
One 20A circuit is going to be limited if you use several appliances at once.
CasualJoe
voted this post useful.
#4
Does a 20 amp breaker trip at exactly 20 amps
Really, PJmax is correct. The unit should have at least two small appliance circuits that should only serve the kitchen. These small appliance circuits are allowed to serve the dining room and other kitchen receptacles.
#5
Member
Thread Starter
Thank you for all the replies.
From this point on, barring separating the circuits to 3 breakers, would nuisance tripping be the only real drawback? (FYI the house was built in 1961 and the panel was recently changed out.)
From this point on, barring separating the circuits to 3 breakers, would nuisance tripping be the only real drawback? (FYI the house was built in 1961 and the panel was recently changed out.)
#6
From what I can tell it is grandfathered. All those outlets can stay as is for now. They won't cause nuisance ground fault tripping but you will get nuisance overload tripping of the panel breaker.
At your leisure you can string additional circuits with an additional one for the bathroom, separate circuits for lights, dishwasher, etc., and also to get more different circuits for the dining room and kitchen receptacles.
Note: If there is any 14 or thinner gauge wiring on that circuit then the breaker must be immediately downgraded to 15 amps.
At your leisure you can string additional circuits with an additional one for the bathroom, separate circuits for lights, dishwasher, etc., and also to get more different circuits for the dining room and kitchen receptacles.
Note: If there is any 14 or thinner gauge wiring on that circuit then the breaker must be immediately downgraded to 15 amps.
#7
(FYI the house was built in 1961
and the panel was recently changed out
As long as the wires are the proper size for the breakers installed and all the connections and devices are in good condition it will likely be OK. However, it is not a good idea to test a wiring system by overloading the circuits.

#8
Member
Thread Starter
Thanks guys. The panel, when I said recently changed out....I think the inspection sticker reads 2019.
There's no FMC in the house. What we do have...it's this NM cable which has this really thin like #16 or #18 bare ground wire.
Is there a common trade name or nick name for this type of cable?
There's no FMC in the house. What we do have...it's this NM cable which has this really thin like #16 or #18 bare ground wire.
Is there a common trade name or nick name for this type of cable?
#10
Member
Thread Starter
When I opened the 20 amp outlet boxes, some contained a separate 15 amp switch/circuit for nearby lights. What I noticed is that the 12 gauge grounds were twisted together, and the 14 gauge grounds were also twisted together. They were not however connected to each other into one wire nut.
Is this practice normal, useful; or relevant in some way?
Is this practice normal, useful; or relevant in some way?
#12
It's grandfathered but today just twisting is not sufficient to bond the equipment grounding conductors. Use a (bare or green) pigtail to join them if the two (you said #12 and #14 respectively) ground bundles won't reach or won't all fit in one wire nut.
Neutrals must be kept separate to the extent that each incoming (feeding) cable's neutral must serve all and only those neutrals in continuing cable(s) served by the matching incoming hot conductor(s)..
Neutrals must be kept separate to the extent that each incoming (feeding) cable's neutral must serve all and only those neutrals in continuing cable(s) served by the matching incoming hot conductor(s)..