Tesla Wall Charger Wire Routing
#1
Member
Thread Starter
Join Date: Sep 2023
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Tesla Wall Charger Wire Routing
Hello everyone. I’m going to be installing a Tesla wall charger. My current plan is to run a 60 AMP breaker with 6 AWG THNN wire from my main panel. I’d like to run the wiring in schedule 40/80 PVC. Looking through the NEC I’m able to use schedule 80 and run my wires above ground. If I use schedule 40 they have to be buried. I haven’t been able to find a specific burial depth. I’ve seen both 18”-24”. Does anyone have a reference for this?
Can someone vector check my plan and see if I’m missing something? My city is currently following the 2020 NEC.
Can someone vector check my plan and see if I’m missing something? My city is currently following the 2020 NEC.
#2
Schedule 40 burial depth is 18" for residential installation and as you know Schedule 80 anything above ground.
#6 Cu THHN with #10 Ground has a 75°C terminal ampacity of 65 amps, so protection with a 60 amp C/B is good...
#6 Cu THHN with #10 Ground has a 75°C terminal ampacity of 65 amps, so protection with a 60 amp C/B is good...
Last edited by Kooter; 09-09-23 at 02:20 PM.
CasualJoe
voted this post useful.
#4
CasualJoe,
Tolyn Ironhand
voted this post useful.