Tesla Wall Charger Wire Routing

Hello everyone. I’m going to be installing a Tesla wall charger. My current plan is to run a 60 AMP breaker with 6 AWG THNN wire from my main panel. I’d like to run the wiring in schedule 40/80 PVC. Looking through the NEC I’m able to use schedule 80 and run my wires above ground. If I use schedule 40 they have to be buried. I haven’t been able to find a specific burial depth. I’ve seen both 18”-24”. Does anyone have a reference for this?

Can someone vector check my plan and see if I’m missing something? My city is currently following the 2020 NEC.


 

Top Answer

 
09-09-23, 09:06 PM
pcboss's Avatar
pcboss
pcboss is offline
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,935
Received 181 Upvotes on 159 Posts
The determination of physical damage is undefined and very subjective.
 
  #2  
Old 09-09-23, 01:11 PM
Kooter's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jan 2003
Posts: 861
Received 88 Upvotes on 81 Posts
Schedule 40 burial depth is 18" for residential installation and as you know Schedule 80 anything above ground.

#6 Cu THHN with #10 Ground has a 75°C terminal ampacity of 65 amps, so protection with a 60 amp C/B is good...
 

Last edited by Kooter; 09-09-23 at 02:20 PM.
  #3  
Old 09-09-23, 01:39 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,158
Received 814 Upvotes on 685 Posts
You are only required to use Sch 80 where the conduit is subject to physical damage.
 
CasualJoe voted this post useful.
  #4  
Old 09-09-23, 02:37 PM
Kooter's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jan 2003
Posts: 861
Received 88 Upvotes on 81 Posts
Bean_Man - What is the total length in feet of your installation from the main panel to the wall charger?
 
  #5  
Old 09-09-23, 06:32 PM
B
Member
Thread Starter
Join Date: Sep 2023
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the feedback. The total length will be 25’ +/- 1’
 
  #6  
Old 09-09-23, 09:06 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,935
Received 181 Upvotes on 159 Posts
The determination of physical damage is undefined and very subjective.
 
CasualJoe, Tolyn Ironhand voted this post useful.
 