Mobile Home Receptacles

Hello all - In March of 2022 I moved into my new mobile home. It was built in December of 2021. The GFCI receptacle in the bathroom (feeds a receptacle to the heat tape under the mobile home) is 12/2 with ground protected by a 20A breaker. To this untrained eye, the GFCI looks like a 15A receptacle. Is there a simple way to know if the receptacle is indeed 15A or 20A? Thanks in advanced for the help. Roger
 

Last edited by the_tow_guy; 11-29-23 at 05:29 AM.
  #2  
Old 11-28-23, 01:58 PM
C
Member
Join Date: May 2015
Location: USA
Posts: 3,150
Received 166 Upvotes on 134 Posts
It's most likely a 15 amp receptacle. On a 20 amp receptacle, one of the two flat slots will be "T" shaped, rather than just a straight slot. On a 20 amp plug, the blade for the hot terminal will be turned 90 degrees to the blade for the neutral. The receptacle has a "T" shaped slot to accept either the 20 amp plug or a more common 15 amp plug.
 
  #3  
Old 11-28-23, 04:33 PM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 27,481
Received 2,107 Upvotes on 1,886 Posts
  #4  
Old 11-28-23, 05:12 PM
C
Member
Join Date: Mar 2007
Posts: 2,503
Received 349 Upvotes on 292 Posts
Not an electrician, but I believe that 15 amp receptacles are OK for use in a 20 amp ckt.
 
CasualJoe voted this post useful.
  #5  
Old 11-28-23, 11:58 PM
A
Member
Join Date: Mar 2014
Posts: 980
Received 159 Upvotes on 132 Posts
15 amp rated receptacles are rated for 20amp pass-tru. 15 amp receptacles are put on 20amp circuits many times and is permitted by code and is safe. You can't put a 20 amp rated receptacle on a 15 amp circuit though just so you know for future use.

Post #3 shows how to tell just by looking at the receptacles.

There are very few devices in a home that would actually require a 20amp receptacle. A 20amp plug would have the neutral prong vertical and the hot prong horizontal which would mean it is rated at 20amp so therefore would only fit in a 20amp rated receptacle. The "T" slot allows a standard plug and a 20amp rated device plug to be inserted into it - "Interchangeability".

Some UPS (Uninterrupted Power Supply) that you would use for a backup in case of a power failure so your computer does not shut down improperly. Some of the more powerful ones do use an actual 20amp plug. It would have a plug like this: One horizontal and one vertical as I described above.


 
  #6  
Old 11-29-23, 12:25 AM
B
Banned. Rule And/Or Policy Violation
Join Date: Oct 2016
Location: United States
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
To check if the GFCI receptacle is 15A or 20A, you can usually find the amperage rating stamped on the device itself. Look closely around the plug holes, or it might be on the backside. If it's a 15A receptacle, it should say 15A, and for a 20A receptacle, it'll say 20A.
 
  #7  
Old 11-29-23, 04:04 AM
R
Member
Thread Starter
Join Date: May 2013
Location: USA
Posts: 140
Upvotes: 0
Received 0 Upvotes on 0 Posts
I learned something new today. Thank you for the education. I can sleep better now.