Burial Wire Labeled As "Low Voltage". Why ?


  #1  
Old 04-13-24, 05:02 AM
R
Member
Thread Starter
Join Date: Apr 2005
Location: MA
Posts: 308
Upvotes: 0
Received 0 Upvotes on 0 Posts
Burial Wire Labeled As "Low Voltage". Why ?

Hello,

Looked at Amazon for some approved direct burial wire to run in a slit in the lawn
from house to an outside lantern pole light.
Probably use a 100 Watt Bulb. 110 V ac

Want to use 14/2 to be on the safe side.

Was surprised to see that they all the direct burial wires are labeled "low voltage" applications.

But, shouldn't (any) 14/2 be fine for 110 V ac ? (it sure is for inside the house)

Why do they label as "low voltage" ?

Thanks,
Bob
 
  #2  
Old 04-13-24, 05:36 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,051
Received 518 Upvotes on 423 Posts
It is the insulation. Low voltage is thinner insulation.
 
CircuitBreaker voted this post useful.
  #3  
Old 04-13-24, 05:44 AM
W
Join Date: Dec 2005
Location: USA
Posts: 3,040
Received 24 Upvotes on 20 Posts
You are looking at the wrong wire. I'm sure an electrician here will correct me if I'm wrong, but the wire you need is UF-B. A slit in the lawn will not meet code requirements. Direct burial line voltage wire must be at least 2' deep.
It would probably be cheaper and easier to convert your post to a low voltage LED.
 
CasualJoe voted this post useful.
  #4  
Old 04-13-24, 11:53 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,401
Received 4,046 Upvotes on 3,630 Posts
Correct.... you need to use 14-2 w/gr UF cable...... 14-2UF/B
 
  #5  
Old 04-13-24, 11:55 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,711
Received 274 Upvotes on 231 Posts
Direct bury can be as shallow as 12" if gfci protected at the source. The max limit on size is 120V 20A circuit.
 
  #6  
Old 04-13-24, 01:25 PM
W
Join Date: Dec 2005
Location: USA
Posts: 3,040
Received 24 Upvotes on 20 Posts
Is that new? I buried a cable 4 years ago to a detached garage. At that time I had three options that I knew of. I could bury it unprotected at 24", in a PVC conduit at 18" and I think (not sure) I could bury it at 12" in concrete.
 
  #7  
Old 04-13-24, 02:34 PM
L
Member
Join Date: Sep 2019
Posts: 136
Upvotes: 0
Received 38 Upvotes on 32 Posts
Not new. Your garage cable is probably a feeder, not a branch circuit, so would not qualify in any case.
 
sdodder voted this post useful.
  #8  
Old 04-14-24, 06:13 AM
T
Member
Join Date: Sep 2015
Location: US
Posts: 1,231
Received 209 Upvotes on 183 Posts
Standard NM cable (Romex) and UF cable (as examples) have insulation rated at 600 Volts maximum. Your cable is probably has insulation rated at 300 Volts maximum. It might appear that 300 volt cable would be suitable, but it is not. Cable for alarm systems is rated 300 Volts and they use 12 or 24 volts.

The 300V marking was removed from low voltage cable a number of years ago. The story I heard was that people were saying, " 300 Volts? I'm only using 120 Volts so this cable is good." The codes are all about keeping you from killing yourself or someone else by electrocution and fire.
 
  #9  
Old 04-14-24, 09:41 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,385
Received 892 Upvotes on 753 Posts
I could bury it at 12" in concrete.
Under 4" of concrete the depth for direct burial cables is still 18" unless it is 20 amps or less and GFCI protected.
 
  #10  
Old 04-14-24, 03:58 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,711
Received 274 Upvotes on 231 Posts
Not new. Your garage cable is probably a feeder, not a branch circuit, so would not qualify in any case.
If the feeder to the garage is a single 120V 20A circuit then the 12" burial depth with GFCI protection at the source does qualify. A feeder of this nature is a branch circuit.
 
 