Running Electrical Wire

Can 14 gauge wire be stapled to the floor joist in a basement? This wire will come from an electrical panel to a receptacle.
 
  #2  
Old 04-16-24, 01:31 PM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 19,190
Received 1,281 Upvotes on 1,219 Posts
Side or bottom of the joist?
 
  #3  
Old 04-16-24, 01:55 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,713
Received 275 Upvotes on 232 Posts
Can be stapled along sides but needs to be at least 1.25 inches from nailing edge of joist. Has to be run through bored holes when going perpendicular across joist. Hole edge need to be back 1.25 inches from nailing edge of joist.
 
  #4  
Old 04-16-24, 05:57 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,428
Received 900 Upvotes on 761 Posts
Individual wires can not be installed without raceway. You need to use a cable such as Non-metallic cable (Romex) if allowed in your area.
 
CasualJoe voted this post useful.
 