12 awg 20A continuous on 25A CB ok?

I need to install a 240v outlet in the garage for 20A continuous service (electrical vehicle charging). It will be a short 15' from the subpanel in the garage. I already have THHN 12 gauge wires and would like to use them. Manufacturer website says 30A max current. For 20A continuous I need 25A CB. Acceptable? Thank you.
 
  #2  
Old 06-19-24, 02:57 PM
L
Member
Join Date: Sep 2019
Posts: 179
Upvotes: 0
Received 49 Upvotes on 40 Posts
Unfortunately not allowed by NEC 240.4(D). 10awg and smaller conductors are treated differently.
 
  #3  
Old 06-19-24, 03:51 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,928
Received 4,139 Upvotes on 3,717 Posts
Unfortunately you will need #10 wiring.
 
  #4  
Old 06-19-24, 04:09 PM
P
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 351
Received 1 Upvote on 1 Post
Thank you for the advice. I will use 10 gauge wires.
 
 