Bad Receptacle Causing Open Neutral?


  #1  
Old 06-23-24, 08:50 AM
C
Member
Thread Starter
Join Date: Apr 2014
Posts: 198
Received 1 Upvote on 1 Post
Question Bad Receptacle Causing Open Neutral?

In the kitchen - have a dedicated circuit that starts with a GFCI receptacle and 2 additional downstream receptacles. Both downstreams stopped working a few days ago. Outlet tester shows the GFCI is wired correctly and the downstreams are showing as open neutrals. I checked all 3 and connections are fine and my multimeter is showing continuity between all the neutrals.

Could this just be a bad receptacle? In a past home, I've dealt with a bad neutral connection being the issue, but wasn't sure if receptacles could poop out in this manner.
 
  #2  
Old 06-23-24, 08:54 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,476
Received 912 Upvotes on 770 Posts
You likely have a bad GFCI.
 
  #3  
Old 06-23-24, 02:46 PM
C
Member
Thread Starter
Join Date: Apr 2014
Posts: 198
Received 1 Upvote on 1 Post
I think you're right. Just from having the breaker off for a couple hours I turned it back on and magically everything started working correctly. I'm going to swap out that GFCI and call it a day.
 
CircuitBreaker voted this post useful.
  #4  
Old 06-23-24, 03:19 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,611
Upvotes: 0
Received 292 Upvotes on 267 Posts
Yes a bad receptacle could be the problem.

A general example (not necessarily yours) -- On the side of an ordinary duplex receptacle unit the tab between the silver screws fractured due to vibration over the years or was broken off. Neutral daisy chained from one receptacle to the next would be broken at that point.
 
  #5  
Old 06-23-24, 03:34 PM
L
Member
Join Date: Sep 2019
Posts: 179
Upvotes: 0
Received 49 Upvotes on 40 Posts
It might be a defective relay in the GFCI.
 
  #6  
Old 06-23-24, 04:43 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,928
Received 4,139 Upvotes on 3,717 Posts
The receptacles operate as mirror images.
The circuitry in the GFI opens neutral and hot to the local receptacle as well as the load receptacles.

If the GFI receptacle works and the others don't.... it is not an internal GFI problem.
 
CircuitBreaker voted this post useful.
 