I am fixing to install a new breaker and run a wire to my deep freeze and one flouresent light. It is a 20 amp breaker and was hoping to use 14-2 wire since i have a whole role laying around. Will this guage be sufficient, Or should I get 12-2?
 
Sponsored Links
  #2  
Old 09-17-01, 02:37 PM
Join Date: Dec 1999
Location: Northeastern NC On The Albemarle Sound
Posts: 10,952
Upvotes: 0
Received 0 Votes on 0 Posts
Cool

You can use 12/2 with a 20 amp (or 15 amp) breaker.
You can use 14/2 with a 15 amp breaker.
You can use 10/2 with a 30 amp breaker.
Use 12/2 in this instance (at least that is what I would do, although I'm not an electrician). 14/2 may be adequate, but one of the pros in here can tell you.
I have no clue what the code is. LOL
Mike
 
  #3  
Old 09-17-01, 03:47 PM
Wgoodrich
Visiting Guest
Posts: n/a
Old Guy, you hit right on the money. Good Code work.

lostintexas, you may use the 14/2 Romex only if you protect it with a 15 amp breaker or fuse. 20 amp breaker or fuse is too high for the ampacity of the 14 awg wire.

Like Old Guy said, I would use 12/2 with a 15 or 20 amp breaker. This freezer is an automatically ran 24/7 appliance that cycles on and off. It uses enough electricity a year to pay the extra cost of the larger 12/2 cable commonly in that first year considering the reduced resistance of that larger wire. Any dollar savings after that is gravy!

Good Luck

Wg
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes