conductor ampacity

Reply

  #1  
Old 10-11-01, 06:31 AM
Visiting Guest
Posts: n/a
Question

If, due to deration, I have used 10/2 to run through conduit, may I connect to it with 12/2 at a junction box that is beyond the conduit- or must the entire circuit be of the same gauge?
 
Sponsored Links
  #2  
Old 10-11-01, 06:42 AM
Member
Join Date: Sep 2000
Location: Fayetteville, NY, USA
Posts: 1,052
Likes Received: 1
You are correct, dropping to a smaller gauge is permitted. I would definitely put a label next to the breaker that reads "20 amp max breaker". I'm not sure if this is a requirement in the NEC, but it's highly recommended. The next guy who comes along may see that beefy #10 connected at the 20 amp breaker and think he can switch to a 30 amp breaker, exposing the #12 wire to 10 more amps than it is rated for, which could overheat and burn the joint down.

Hope that helps.

Juice
 