Hello;

I am running 4 new circuits for a kitchen remodel.

Can I drill a 1" hole thru the joists in an unfinished basement and run these to the kitchen from the breaker panel approx 30 feet?
Or more importantly, do I have to worry about derating the cable due to cabling effect?

Im using 12/2NMB. The wires will obviously be together but not bound together with ties or anything.

Thanks in advance
Anthony
 
Sponsored Links
  #2  
Old 02-25-02, 11:25 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
The answer is yes to the 1" hole, but I wouldn't do it anyway.

Drill a separate 5/8" hole for each 12/2 cable. Drill each hole dead center (vertically) in each joist, and don't drill in the middle third of the span. Separate each hole by a couple of inches. These guidelines will help maintain the strength of your joists.

No derating will be necessary.
 
  #3  
Old 02-25-02, 11:32 AM
P
POS Guy
Visiting Guest
Posts: n/a
Thanks John;

But if I choose to go with a 1" hole, do I have to derate?

Anthony
 
  #4  
Old 02-25-02, 02:31 PM
S
Sketchy
Visiting Guest
Posts: n/a
You never need to derate Romex running through holes in wood, unless it is tightly packed together for a run of more than 24" (or maybe it's 16"?). Between the joists, the 4 cables will naturally hang together, but that's not considered tight enough to be subject to derating.

-- Jim
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: