How many wires in conduit
Can i run 3-10 awg and 2-12 awg in an 1/2 inch conduit? How about 2-10 awg and 2-12 awg?
Thanks
Thanks
#5
Member
Thread Starter
Join Date: May 2001
Location: USA
Posts: 124
Upvotes: 0
Received 0 Upvotes
on
0 Posts
What if both circuits wont be used at the same time? The 30 amp circuit powers a 220 heater in a garage which is used 5 times a year at best and the 20 amp circuit will be for workshop outlets, drills, sanders, and the what not.
#7
The ampacity deration that I was referring to is table 310.15.B.2. As far as I know there is no credit concerning this deration table concerning non coincidental loads. Whether you use them or not if they are current carrying loads they are current carrying loads whether they are carrying current at a specific time or not.
Hope this helps
Wg
Hope this helps