How many wires in conduit
Old 02-25-02, 04:47 PM
P
Can i run 3-10 awg and 2-12 awg in an 1/2 inch conduit? How about 2-10 awg and 2-12 awg?
Thanks
Old 02-25-02, 04:53 PM
resqcapt19
What type of conduit? What type of wire?
If it is thinwall (EMT) and THWN wire 5 #10s are permitted in a 1/2" conduit. If it is schedule 40 PVC and type THW, only 3 #10s fit.
Don(resqcapt19)
Old 02-25-02, 06:05 PM
P
Thank you it was Thinwall EMT with thwn wires
Old 02-26-02, 01:55 PM
Wgoodrich
Be careful installing that many conductors in a conduit. If you install more than three conductors in a raceway you must start reducing ampacity of those conductors.
Good Luck
Wg
Old 02-26-02, 02:22 PM
P
What if both circuits wont be used at the same time? The 30 amp circuit powers a 220 heater in a garage which is used 5 times a year at best and the 20 amp circuit will be for workshop outlets, drills, sanders, and the what not.
Old 02-27-02, 05:06 PM
P
Just bumpin post back up
Thanks
Old 02-27-02, 05:25 PM
Wgoodrich
The ampacity deration that I was referring to is table 310.15.B.2. As far as I know there is no credit concerning this deration table concerning non coincidental loads. Whether you use them or not if they are current carrying loads they are current carrying loads whether they are carrying current at a specific time or not.
Hope this helps
Wg