Doesn't the number of conductors also get impacted by the type of conduit. PVC is lis

Doesn't the number of conductors also get impacted by the type of conduit. PVC is lis

Reply

  #1  
Old 03-08-02, 08:53 AM
joelp
Visiting Guest
Posts: n/a
Doesn't the number of conductors also get impacted by the type of conduit. PVC is lis

John, I am a novice to some of these things, but I was reviewing the NEC Code Book and came up with two different tables. One for PVC, see attachment

http://www.jhlarson.com/data_tables/pvcfill.htm

Versus:

http://www.elliottelectric.com/1050/...onduitFill.asp

There is a definite difference in the number of wires that can be run through EMT versus PVC due I guess to the wall thickness.

At the 1/2" diameter, everything in PVC seems to be 1 less than EMT. Just an observation.

I guess your no was with regard to her specific issue.

Thanks for helping to explain
Joel
 
Sponsored Links
  #2  
Old 03-08-02, 08:58 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
Sorry Joel. You are correct that the fill calculations are affected by type of conduit. There are about a dozen different tables in the NEC.

The other thread also was talking about ampacity derating, and I mistakenly thought you were asking whether that was affected by type of conduit.
 
  #3  
Old 03-08-02, 10:18 AM
joelp
Visiting Guest
Posts: n/a
No need for an apology. I just was concerned that I may have been mistaken. This forum is great. Keep up the good work.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: