First post here on this great forum. I really appreciate having the expert advice available on these DIY forums.
I have a plan to add power to the new workshop I'm building, and I'd like to run it by here for your concurrence.
1800-sq ft high-bay detached workshop will have both woodworking and metal/engine tools, climate control (possibly heat pump) and several 3-5 hp single and 3-phase motors (rotary phase converter).
I plan to add a 240V/100A breaker to my 200A service entrance panel at the house. Will run #2AWG THWN (2 black, 1 white, plus #6AWG equipment ground conductors) underground in 1-1/2 inch PVC conduit buried 18" for 125 ft. At shop, will install a 200A SEP I already have, with a 200A service disconnect/breaker. Will isolate the neutral buss from ground and will install two grounding electrodes 6-ft apart at shop to ground the EGC buss there. Will add 20A and 30A circuits as needed in shop using NMC and quad receptacles.

See anything (A) unsafe, (B) non-NEC compliant, or (C) wasteful? I'd appreciate your comments. Thanks again for being there.
Tom C
 
Sponsored Links
  #2  
Old 03-28-02, 11:04 AM
P
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
Received 0 Votes on 0 Posts
Table 430-148 of the NEC lists 28 amps as the full-load current of a 5 HP single-phase 230 volt motor. The starting surge may be 300% of this value or approx 100 amps.If you add this to a 5HP motor already running, which is 130 amps. you may trip the 100 amp breaker at the service.On motor-feeders the NEC permits a circuit-breaker with a rating that exceeds the rating of the feeder conductors,ex., a 150 amp breaker protecting conductors rated at 100 amps.I believe a motor-feeder calculation is needed.I suggest you submit a detailed list of the loads you plan on connecting to the feeder. Another question is the maximum load (compared to the total connected load) that will be in operation at a given time. This depends upon how you will utilize the motor-driven equiptments. Please reply-thanks.
 
  #3  
Old 03-28-02, 12:22 PM
Tom Carter
Visiting Guest
Posts: n/a
Worst case might be:

lights on plus maybe fan, radio-2KW;
dust collector running-3hp, 230V;
start 3-phase rotary convertor, then start 5 hp 3-phase radial arm saw.

One unknown might be the 5 hp compressor with a mind of its own kicking in.

Clearly, if I decide on a heat pump, that would be too much.

Think I should revisit Plan A for dedicated 200A service from the electric co-op?

Trying the pic again--see attachment.
Tom
 
  #4  
Old 03-28-02, 05:50 PM
HandyRon's Avatar
Member
Join Date: Dec 2001
Location: New York
Posts: 1,365
Received 0 Votes on 0 Posts
Because of the length of the run. I would suggest copper conductors sized as you mention, not aluminum.
Service size is a question. Practically adding the loads you will have on continuously, may be a concern because of starting current of the larger motors. 5HP, 3ph radial arm saw seems pretty big!
 
  #5  
Old 03-28-02, 06:29 PM
MTgets
Visiting Guest
Posts: n/a
Aside from the service questions, one minor issue:
Why are you running NMC to you recepticles? In VA can you not run EMT? I would recommend EMT conduit in a shop environment. sounds like you are doing some serious fabricating in there. Cost difference is slight but well worth it.
 
  #6  
Old 03-28-02, 08:01 PM
HandyRon's Avatar
Member
Join Date: Dec 2001
Location: New York
Posts: 1,365
Received 0 Votes on 0 Posts
If interior will be finished with panelling or wall board, NM cable is fine and much easier to install.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: