Replacing old 2 prong outlets


  #1  
Old 03-31-02, 04:02 PM
dylan925
Visiting Guest
Posts: n/a
Replacing old 2 prong outlets

When replacing old 2 prong outlets that are fed by armored cable is it correct to connect the ground screw on the new outlet to the box? This assumes that I meter from hot to box and get voltage.

I have spoken to one electrician that tells me that research has been done showing that the old armored cable can become red hot if there is a ground fault. With this in mind he said the correct thing to do is jump the neutral to the ground screw.

I am assuming 120v circuits and not GFCI.

What's the code say guys? Thanks
 
  #2  
Old 03-31-02, 05:19 PM
HandyRon's Avatar
Member
Join Date: Dec 2001
Location: New York
Posts: 1,365
Received 0 Votes on 0 Posts
Absolutely DO NOT connect the neutral to ground at an outlet.
Assuming the armored cable is terminated well, yes connect the ground screw on the outlet to the armored cable through the box.
 
  #3  
Old 03-31-02, 07:00 PM
M
Member
Join Date: Jan 2002
Location: Illinios
Posts: 258
Received 0 Votes on 0 Posts
I agree with Ron The first electrician was totally WRONG!!
 
  #4  
Old 04-01-02, 07:56 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 1 Vote on 1 Post
Jumpering the neutral and grounding connections is just about the stupidest thing you can do. To do so very significantly increases the electrocution danger in your home. It's much better to leave the grounding connection unconnected than it would be to use the jumper.
 
 