underground wiring

Reply

  #1  
Old 05-01-02, 06:21 PM
T
tstokka
Visiting Guest
Posts: n/a
underground wiring

Just wondering what size wire to use if I were to put power out 150ft. I would need at least 40-50 amps at the end of the run. could use two or more runs, 20 amps minimum per run.
 
Sponsored Links
  #2  
Old 05-01-02, 07:49 PM
W
Wgoodrich
Visiting Guest
Posts: n/a
The NEC does not allow you to parallel conductors smaller than a 2 awg conductor.

40 amp = 8 awg copper or 6 awg aluminum

50 amp = 6 awg copper or 4 awg aluminum

Good Luck

Wg
 