electrical service to garage

Reply

  #1  
Old 02-14-00, 09:37 PM
Guest
Visiting Guest
Posts: n/a
Post

I would like to run 220v electrical service from the main house panel underground to my garage. What size and type of wire would be recommended?

------------------
 
  #2  
Old 02-15-00, 09:27 PM
Guest
Visiting Guest
Posts: n/a
Post

hello Service4Homes,
this would all depend on what u plain on running in the garage, and what size sub panel u have (1 u r puttin in garage. let me know this and ill help u out.
 
  #3  
Old 02-15-00, 10:04 PM
Guest
Visiting Guest
Posts: n/a
Post

A hot water heater, electric stove, electric dryer and a heat pump plus lights.
 
  #4  
Old 02-16-00, 10:10 PM
Guest
Visiting Guest
Posts: n/a
Post

hello service,
from your info id put nothing less than a 100 amp 20 space sub panel in this will supply u with enough for what u r adding now and still leave u room 4 future. the 100 amp will require a 100 amp 2 pole breaker installled in existing panel with #3 thhn used 4 the 2 hots and nutural and a #6 for the ground. this is if u r useing conduit. if u plain on useing SE cabel u will need to drive a ground rod at the sub and ground it useing #6. heres a money saveing tip check with your local building authority and c if they will allow u to use #4 thhn on a 100 amp sub here it is allowed in a residance. if u need any more help feel free to post or e-mail me.
 
 