220 breaker


  #1  
Old 06-12-02, 06:37 PM
Cableguy
Visiting Guest
Posts: n/a
Unhappy 220 breaker

I bought a trailor and I have a problem. My dryer and my hotwater heater are wired on the same 40 amp circuit and if I use them both it blows. Is it ok to put in a higher amp breaker in or should I go out and buy a new box and split them up?
 
  #2  
Old 06-12-02, 07:46 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Do not put in a larger breaker. That's a recipe for burning your house down.

The dryer and hot water heater should each have their own 30-amp circuits. Neither should be on a 40-amp circuit. It's possible that this is already a fire waiting to happen.
 
 