POWERING GARAGE
#1

HOW DO I WIRE TECH.CABLE FROM 60amp BREAKER IN HOUSE BOX TO 60amp BREAKER IN BOX 1 OF GARAGE TO TAKE OFF BOX 2 IN GARAGE ?
(TECH CABLE RED-BLACK-BLUE-COPPER)
(TECH CABLE RED-BLACK-BLUE-COPPER)
#2

Andy,
First, and most important you do not have an approved electrical premise wiring cable.
If you want to be able to feed a 60 amp subpanel you will need either at 6/3 romax cable or use conduit with #6 rated cable.
Since I don't know the distance nor the route between your panel and the subpanel it is very difficult to tell you how to install the proper wiring.
I also don't understant what you are referring to as "taking off box 2 in garage.
If you can provide a little more information I or someone can better help you.
First, and most important you do not have an approved electrical premise wiring cable.
If you want to be able to feed a 60 amp subpanel you will need either at 6/3 romax cable or use conduit with #6 rated cable.
Since I don't know the distance nor the route between your panel and the subpanel it is very difficult to tell you how to install the proper wiring.
I also don't understant what you are referring to as "taking off box 2 in garage.
If you can provide a little more information I or someone can better help you.