GFI's
#1
GFI's
It seems I have seen two different answers to the guestion of running a ground from a GFI. To protect the outlets downstream, do you or do you not connect a ground wire to and from the GFI that is protecting the downstream outlets?
#2
A GFCI only needs a hot and neutral (grounded) conductor to operate. The grounding or safety conductor which is normally bare or green, is great to have, but not needed for operation of the GFCI itself. So if you have it, yes extend and terminate the grounding conductor on every device and metal box (if you have them) for safety and ground reference.
#3
YOU MAY NOT CONNECT the grounding wire from the GFI to the downstream receptacles. This is a violation of code!!
Article 406.3 (D) covers replacement of receptacles. Article 406.3 (D) (3) a-c Tells you specifically what to do when replacing NON-Grounding type receptacles and I am assuming that's what we are talkng about here. You can replace the feed receptacle with a GFI and tie the downstream receptacles to the load side of the GFI. YOU MAY NOT however, run a ground from that GFI to the downstream receptacles. The Receptacles must also be marked "GFCI PROTECTED" and "NO EQUIPMENT GROUND"
Article 406.3 (D) covers replacement of receptacles. Article 406.3 (D) (3) a-c Tells you specifically what to do when replacing NON-Grounding type receptacles and I am assuming that's what we are talkng about here. You can replace the feed receptacle with a GFI and tie the downstream receptacles to the load side of the GFI. YOU MAY NOT however, run a ground from that GFI to the downstream receptacles. The Receptacles must also be marked "GFCI PROTECTED" and "NO EQUIPMENT GROUND"
#4
Sparksone42, you made the assumption that boman doesn't have a valid equipment grounding conductor to his GFCI. If the assumption is true, then you are correct. If the assumption is not true, then Ron is correct.
#6
So you did. I missed that. It is certainly not my intention to rub you the wrong way, and I welcome your input. I won't mind it a bit if you choose to disagree with anything I say.
Last edited by John Nelson; 07-19-02 at 01:11 PM.
#7
I assumed that he was not transitioning from two prong to three prong, but just installing new branch wiring. Hence my earlier comment.
I also have no problem with any comments, but you might consider giving the benifit of the doubt and explaining that my previous comment would be the method for a new branch circuit, rather than SHOUTING. I have learned from this thread, that I need to be more careful not to assume the application.
boman,
Could you fill us in as to your application, then we will attempt to offer the correct solution.
I also have no problem with any comments, but you might consider giving the benifit of the doubt and explaining that my previous comment would be the method for a new branch circuit, rather than SHOUTING. I have learned from this thread, that I need to be more careful not to assume the application.
boman,
Could you fill us in as to your application, then we will attempt to offer the correct solution.
#8
I tried to post this yesterday, but kept getting knocked off here. Anyway, I should have explained that I was talking about a situation where wiring was being upgraded to 3 prong outlets with 12/2 with ground from the main service panel. I should have stated that to stay within the context of the discussion, I guess. Sorry to have caused any .......confusion.
#9
Sounds like you have a grounding conductor run with your new wiring from the main panel. If this is the case, then follow my original suggestion of connecting the grounding (safety) conductor at each receptacle. This bonding is required by code, when the grounding conductor is available on new wiring. There are certain exceptions for old exisitng wire without a grounding conductor.