I have a Ademco Vantage 4110 (4110xm) with a 4127 key pad , It is now in the ready mode but I do not have the master code can you help me obtain that so I can arm it . thank you (whlman500)
Old 07-29-04, 04:37 PM
Received 265 Upvotes on 244 Posts
Disconnect the battery, then the ac power. Withing 50 seconds of power up, press * + # at the same time. This should (assuming no program lockout by the previous installer) kick it into program mode. Press #20. The key pad will then read back the master code. Exit with *99.
Old 07-29-04, 06:51 PM
whlman500
MrRonFl I did that and it comes up with 06 and no AC that is still with the power on but I do not see a master code ? am I doing this right > whlman 500
Old 07-30-04, 03:52 PM
whlman500
I tried it again and it came up 00-02-07-06 is that the master code # ?? can I arm the system with it ? Thanks whlman500
Old 07-30-04, 04:02 PM
Ok, lets try this again. When you did powerup * + #, the next thing you should have seen is a 20 on the screen. If you did not see this, then you were not in program mode. It is very possible that local access programming has been locked out of this panel by the prior installer using download software.
If you saw a 20; the next key strokes should be #20. This will display the master code 1 digit at a time with a "ping" after each number and a triple ping after the final number. If you heard these sounds, and saw only sixes, then the master code is 6666.
the "no ac" thing is just an indicator that the system is not in normal running mode.
Ademco programming procedures have a bit of a learning curve to them.
Old 07-30-04, 04:33 PM
Yup, your magic number is 0276. On these older ademco panels master code and go to program code are the same number. A lot of people will use the master code to program a user code (the ademco/honeywell website has user manuals for free download, not installer manuals, though) for everyday use, and seal the master code in an envelope in some safe place.
whlman500
Yes the 20 came up and it did what you said would come up it ended with a 06 and 3 beeps
Old 07-30-04, 04:42 PM
whlman500
MrRonFL: thanks you were a big help I sure appreciate you takeing the time to help me. whlman500
Old 07-31-04, 10:32 AM
whlman500
Still having problems now that I have the master code 0276 ,when I power up and the ready sign comes up then the 09 not ready comes up (troubleshooting says wireless has not heard transmission for 12 hrs I do not have a wireless in system ?)If I can get this solved and the ready comes on how can I arm the system now that I have the master code. any help would be appreciated thanks < whlman500>
Old 07-31-04, 12:52 PM
whlman500
I was able to arm the system but after about 15 sec 09 alarm comes on how do you shut alarm off without turning off power? and how do I get rid of 09?Thanks. <whlman500>
Old 07-31-04, 06:44 PM
whlman500
P.S I do not have a RF receiver wired in control panel (wireless) all I want to do is use my 6 zones thanks <whlman500> I want to delete check 09
Old 07-31-04, 10:47 PM
Assuming that it never had wireless, check 09 can also mean keyswitch is enabled but not connected. It is possible that you may have inadvertantly turned on either option when you were in program mode. I don't have my copy of the manual handy, but I think that if you go to program (master code + 8 + 0) then check option 22 you will likely find that there is a 1 instead of a 0. There is a similar line for wireless, but I don't have the program map handy to give you specifics.
Disarming all ademco style systems is command based (code + off[1])
Old 08-01-04, 09:01 AM
See if this helps:
(If you want the full manual, go to http://manuals.safewatchservice.com)
Ademco 4110XM Program Sheet
Enter Program 1. Master Code + 8 + 0 + 0 (Display should show 20)
or Power down then back up and press * and # within 1 minute
(If exiting programming you can re-enter within 1 minute by pressing * and #)
Move to Location * + Location
View Location # + Location (Display will read off one digit at a time)
Exit Program 1. *98 OR 2. *99 if needing to re-enter programming later by Code + 8 + 00
Hex Program Hex A = # + 10 B = # + 11 C = # + 12 D = # + 13 E = # + 14 F = # + 15
If trying to enter a location and display shows FF that location does not exist (older version)
*20 Master Code I _ _I _ _I _ _I _ _I (Default is 4110)
*21 Quick Arm Enable I _ 1 _I (0 = No 1 = Yes)
*22 Keyswitch Enable I _ 0 _I (0 = No 1 = Yes)
*23 Force Bypass Enable I _ 0 _I (0 = No 1 = Yes)
*24 RF House Code I _ 0 _I _ 0 _I (if using 5700 Wireless enter 01 to 31)
*27 Audible Exit Warning I _ 1 _I (0 = No 1 = Yes)
*28 Confirmation of Arming Ding I _ 0 _I (0 = No 1 = Yes)
*29 Fire Sounder No Timeout I _ 1 _I (0 = No 1 = Yes)
*30 Alarm Bell Timeout I _ 2 _I (1 = 4 min, 2 = 8, 3 = 12, 4 = 16)
*31 Zone 1 Definition I _ ? _I
0 = Zone Disabled 5 = Trouble by Day
1 = Entry/Exit 6 = 24 hr Silent (Holdup)
2 = Not Used 7 = 24 hr Audible (Police Panic)
3 = Instant/Perimeter 8 = 24 hr Auxiliary (Medical)
4 = Interior/PIR 9 = Fire without timeout (Smokes)
10 = Interior with Delay
*32 Zone 2 Definition I _ ? _I
*33 Zone 3 Definition I _ ? _I
*34 Zone 4 Definition I _ ? _I
*35 Zone 5 Definition I _ ? _I (Smoke Detectors MUST use this Zone)
*36 Zone 6 Definition I _ ? _I
*37 Zone 7 Definition (Panic * & #) I _ 7 _I (7 = Audible, 6 = Silent)
*38 Entry Delay I _ 2 _I (1 = 20 sec, 2 = 30, 3 = 45, 4 = 60, 5 = 90)
Exit Delay = Entry Delay + 15 seconds
*39 Zone 3 Response to open l__0__l (0 = 400ms, 1 = 10ms)
*40 PABX Access Code I _ _I _ _I _ _I _ _I (If 9 is needed to dial add here)
*41 Primary Phone (12 digits) I _ _I _ _I _ _I _ _I _ _I _ _I _ _I _ _I _ _I _ _I _ _I _ _I
End Phone Number with * # + 11 = * # + 12 = # # + 13 = 2.5 second pause
*42 Secondary Phone I _ _I _ _I _ _I _ _I _ _I _ _I _ _I _ _I _ _I _ _I _ _I _ _I
(Pager only available on VERY new 4110XM's, pager will not work if Account starts with 0)
*43 Subscriber Account I _ _I _ _I _ _I _ _I
*44 Report Format I _ 7 _I 0 = 3/1, 4/1 Ademco L/S Standard
1 = 3/1, 4/1 Radionics Standard
2 = 4/2 Ademco L/S Standard
3 = 4/2 Radionics Standard
6 = 4/2 Ademco Express
7 = Contact ID
8 = 3/1, 4/1 Ademco L/S Expanded
9 = 3/1, 4/1 Radionics Expanded
*45 Phone Sys Select I _ 1 _I 0 = Pulse 1 = DTMF (No Watts Line)
2 = Pulse 3 = DTMF (Watts Line)
*46 Sescoa/Radionics Select I _ 0 _I (0 = Radionics 1 = Sescoa)
*47 15 Sec Burg Dial Delay I _ 0 _I (0 = No 1 = Yes)
*48 Periodic Test Message I _ 0 _I (0=None, 1=24 Hrs, 2=Weekly)
*49 Split/Dual Reporting I _ 0 _I (0 = Backup Report Only)
To Primary Phone To Secondary Phone
1 = Alarms, Restore, Cancel All Other Reports
2 = All Reports except Open/Close, Test Open/Close, Test
3 = Alarms, Restore, Cancel All Reports
4 = All Reports except Open/Close, Test All Reports
5 = All Reports (Dual Reporting) All Reports
The following is only available with very new 4110XM's, use 6 if programming Pagers
6 = All reports except Open/Close Alarms, Open/Close, Troubles
7 = All reports Alarms, Troubles
8 = All reports Alarms, Open/Close, Troubles
9 = All reports except Open/Close Alarms, Open/Close for Users 5–25, Troubles
*50 Keypad Medical/Fire I _1 _I 1 & * (Silent, sends 95, use as Medical Panic)
I _1 _I 3 & # (Audible, sends 96, use as Fire Panic)
*51 Zone 1 Report Code I _1 _I _ 0 _I
*52 Zone 2 Report Code I _1 _I _ 0 _I
*53 Zone 3 Report Code I _1 _I _ 0 _I
*54 Zone 4 Report Code I _1 _I _ 0 _I
*55 Zone 5 Report Code I _1 _I _ 0 _I
*56 Zone 6 Report Code I _1 _I _ 0 _I
*57 Zone 7 Police Panic Report Code I _1 _I _ 0 _I
*58 Zone 8 Duress Report Code I _1 _I _ 0 _I
*59 Zone 9 Receiver Fail Report Code I _0 _I _ 0 _I
*60 Trouble Report Code I _1 _I _ 0 _I (Fire Trouble)
*61 Bypass Report Code I _0 _I _ 0 _I
*62 AC Loss Report Code I _1 _I _ 0 _I
*63 Low Bat Report Code I _1 _I _ 0 _I
*64 Test Report Code I _0 _I _ 0 _I
*65 Open Report Code I _ 0 _I
*66 Close Report Code I _ 0 _I
*67 RF Xmtr Low Bat I _0 _I _ 0 _I
*68 Cancel Report Code I _1 _I _ 0 _I
*69 Group Restores Trouble/Bypass I _ 0 _I
*70 Alarm Restore Code I _ 0 _I
*71 Trouble Restore Code I _0 _I _ 0 _I
*72 Bypass Restore Code I _0 _I _ 0 _I
*73 AC Restore Code I _0 _I _ 0 _I
*74 Low Bat Rest Code I _0 _I _ 0 _I
*75 RF Low Bat Restore Code I _0 _I _ 0 _I
Wireless Zone Programming
*76 to *79 only available with 4281L (Low) Receivers
*76 to *83 only available with 4281M (Medium) or 4281 (High) Receivers
Zone 10 to 13 = Delay zone Zone 56 to 61 = Day Zone
Zone defines type of sensor Zone 14 to 29 = Instant Zone 62 = 24 hr Audible
Zone 30 to 47 = Interior/PIR Zone 63 = Programmed in *92
Zone 48 to 55 = Fire
*76 1st Wireless Zone Definition I _ ? _I _? I Zone Number
I _ 1 _I _0 I Report Code
*77 2nd Wireless Zone I _ ? _I _? I Zone Number
*78 3rd Wireless Zone I _ ? _I _? I Zone Number
*79 4th Wireless Zone I _ ? _I _? I Zone Number
*80 5th Wireless Zone I _ ? _I _? I Zone Number
*81 6th Wireless Zone I _ ? _I _? I Zone Number
*82 7th Wireless Zone I _ ? _I _? I Zone Number
*83 8th Wireless Zone I _ ? _I _? I Zone Number
*92 Zone Response 63 I _0 I (0, 6, 7, 8, 9 only)
*93 Reports Per Armed Period l__0__l (0 = 10 Reports, 1 = Unlimited)
*94 Download Phone Number I _1 _I _ 8 _I _0 _I _ 0 _I _6 _I _ 8 _I _2 _I _ 1 _I _6 _I _ 9 _I _0 _I _ _I
*95 Ring Count I _# 15 _I (0 to 15 15 = Answer Machine)
*96 Reinitialize Download (No Value needed, keypad will just beep)
*97 Default Panel (No Value needed, keypad will beep and default panel)
*98 Exits Program Mode (Will not allow re-entry with Installer Code + 8 + 0 + 0)
*99 Exits Program Mode (Will allow re-entry with Code + 8 + 0 + 0)
Thought I'd throw this in too:
Ademco 4111XM Trouble Display
6F Long Range Radio trouble
NO AC AC Power Failure
BAT Panel Battery low
BAT 01 - 30 Zone has low battery
BAT 00 Low Remote Keypad battery
Check 01 - 30 Zone is not communicating with panel
Check 9 Wireless Receiver or Module failure (check sections 22, 24, 25)
Check 70 Supervised Bell Circuit trouble (Make sure *91 is 0 to prevent this)
D1 System is in wait mode, if remains system has an internal problem
System Busy System is in wait mode, if remains system has an internal problem
CA Alarm was canceled, this is not a system trouble
Canceled Alarm Alarm was canceled, this is not a system trouble
CC Panel is being downloaded by Tech Support
EA Exit Alarm, this is not a trouble, system was armed
and door wasn't closed before Exit Delay expired
FC Fail to Communicate
E4 More wireless zones programmed than Low receiver capable of using
E8 More wireless zones programmed than Medium receiver capable of using
OC Open Circuit, bad keypad wire
Beep every 40 sec System is in Test Mode (Press Code + 1 to exit)
Reset Smoke 4-digit code + 1 (OFF) twice to turn off siren and reset smoke
(If this does NOT reset smoke detector set for service, smoke is bad)
(If Wireless)
Smoke Batteries Remove old batteries, hold Smoke test button 30 seconds, add new batteries
Old 08-01-04, 02:52 PM
whlman500
I sure do appreciate the help you guys have given me but I just can't get that 09 check out it keeps coming up I power up annd wait 1 min then it will say ready then 30sec or less check 09 comes up or if I go to arm real fast the alarm will go off real fast maybe I should get new control panel & pad thanks for your help < whlman500 > P.S I have all off the manuels for this system 4110XM installation, security system user's manual
Old 08-01-04, 07:56 PM
You could always try defaulting the panel. You will have to reprogram it, but of course, you'll have to program a new one anyway. Might be worth a try?
Good luck!
Old 08-02-04, 11:42 AM
whlman500
MrRonFL & SafeWatch I think I got it I went into program and field 24 and programed 00 that field was for wireless now the system can arm and the check 09 does not come up I hope this info will help someone later thanks again. < whlman500>
Old 08-02-04, 04:07 PM
whlman500
I still need some help: I can not bypass zones useing directions. (user code-bypass key-zone#) also when I powerup useing *# to get into program mode I have to repower to go back to normal. also can not go into program mode from ready.(useing master code+code key+0 what am I doing wrong? thanks. <whlman500>
Old 08-03-04, 07:05 PM
Exit program mode with *99. This will allow reentry via MC+8+00
With all ademco products, your keystrokes have to be in a continuous string. More than about 1-1/2 seconds hesitation between keystrokes kicks you out of whatever you are trying to do.
Old 08-03-04, 07:25 PM
whlman500
MrRonFL: Thanks for the advice it works fine now. < whlman500>
Old 08-06-04, 09:07 PM
whlman500
I have one more Q .after the alarm is set I wait about 5 min then I open the door in 15 sec the key pad will sound then about 45 sec later the alarm will sound can I get it to have a instant alarm ? Thanks < whlman500 >
  #21
Old 08-06-04, 10:32 PM
Yes, just arm it in instant mode instead of away or stay.
  #22
Old 08-07-04, 08:35 AM
whlman500
Thanks MrRonFL I will try that. < whlman500>
  #23
Old 08-12-04, 07:23 PM
whlman500
I have another question can you connect 2 door contacts in tandem to 1 zone, or do you have to run a new line to the control panel for that contact. Thanks (whlman500)
  #24
Old 08-13-04, 03:00 PM
Yup, you sure can. Most likely your windows are already done that way. The wires just need to be tied together so that the switches are in series (not parallel). Just remember that if you tap a zone that has a delay, the new opening will also have that delay.
  #25
Old 08-13-04, 08:42 PM
whlman500
MrRonFL: thanks I will give it a try . <whlman500 >