Vista 20 Programming
Old 02-01-05, 08:14 PM
BVM
Question Vista 20 Programming
Does anyone know the setup for field 35 on a Vista 20. I have the manual for the Vista 20 SE that shows you can enter a two digit code to represent seconds but my control only accepts single digits that I assume are coded. Also my control does not show field 34 as exit delay. Is it programmable? Field 36 does not represent delay 2. Is it programmable?
Old 02-02-05, 07:17 AM
The Vista 20 programming is different than the Vista 20SE programming:
Ademco Vista-20 Program Sheet
Enter Program 1. 4112 + 8 + 0 + 0 (Display should show 20)
or Power down then back up and press * and # within 1 minute
(If exiting programming you can re-enter within 1 minute by pressing * and #)
Move to Location * + Location
View Location # + Location (Display will read off one digit at a time)
Exit Program 1. *98 OR 2. *99 if needing to re-enter programming later by Code + 8 + 00
If trying to enter a location and display shows FF that location does not exist (older version)
*20 Installer Code l__4__l__1__l__1__l__2__l
*21 Quick Arm Enable l__1__l Partition 1 (0=No, 1=Yes)
l__1__l Partition 2 (0=No, 1=Yes)
*22 RF System Type l__0__l (0=None, 1=5800 Receiver)
*23 Forced Bypass Enable l__0__l Partition 1 (0=No, 1=Yes)
l__0__l Partition 2 (0=No, 1=Yes)
*24 RF House Code l__0__l__0__l (01 to 31)
Note: Partition 2 RF House ID = Partition 1 House ID +1
*25 Wired Expansion Module l__0__l (0 = None 1 = 4219 2 = 4229 3 = 4204)
*26 Chime by Zone l__0__l (0 = No, 1 = Yes)
*27 X-10 House Code l__0__l 0 = A 1 = B 2 = C 3 = D 4 = E 5 = F
6 = G 7 = H 8 = I 9 = J #10 = K #11 = L
#12 = M #13 = N #14 = O #15 = P
*28 4285 Voice Module Access Code l__0__l__0__l (Disabled)
Note: Allows access to Voice module, 1st digit = 1 to 9 2nd digit = # + 11 for * or # + 12 for '#'
*29 Output to Long Range Radio l__0__l (0 = No, 1 = Yes)
*30 Keyswitch Enable Zone 7 l__0__l (0 = No, 1 = Yes)
*32 Single Alarm Sounding/Zone l__0__l (0 = No, 1 = Yes)
*33 Fire Sounder Timeout l__0__l (0=Timeout, 1=No Timeout)
*34 Alarm Bell Timeout l__1__l (0=None, 1=4 min, 2=8, 3=12, 4=16)
*35 Entry Delay l__2__l Partition 1 0 = No Delay
l__2__l Partition 2 1 = 20 seconds
2 = 30 seconds
3 = 45 seconds
(Exit Delay = Entry Delay + 40 Seconds) 4 = 60 seconds
5 = 90 seconds
*36 Audible Exit Warning l__1__l Partition 2 (0 = No, 1 = Yes)
l__1__l Partition 2
*37 Confirmation of Arming Ding l__0__l__0__l (0 = No, 1 = Yes)
*38 Power Up in Previous State l__0__l (0 = No, 1 = Yes)
*40 PABX Access Code l__ _ _l__ _ _l__ _ _l__ _ _l (If 9 is needed to dial add here)
*41 Primary Phone (12 digits) l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l
End Phone with * # + 11 = * # + 12 = # # + 13 = 2.5 second pause
*42 Secondary Phone l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l__ _ _l
Note: The original Vista-20 cannot do Pagers, only Vista-20SE's can
*43 Primary Account Partition 1 l__ _ _l__ _ _l__ _ _l__ _ _l (Last 4 of Account)
Note: Hex A = # + 10 B = # + 11 C = # + 12 D = # + 13 E = # + 14 F = # + 15
*44 Secondary Account Partition 1 l__ _ _l__ _ _l__ _ _l__ _ _l (Do not Program)
*45 Primary Account Partition 2 l__ _ _l__ _ _l__ _ _l__ _ _l (Do not Program)
*46 Secondary Account Partition 2 l__ _ _l__ _ _l__ _ _l__ _ _l (Do not Program)
*47 Phone Sys Select l__1__l 0 = Pulse
1 = DTMF (No Watts Line)
2 = Pulse
3 = DTMF (Watts Line)
*48 Report Format l__7__l Partition 1 0 = 3/1, 4/1 Ademco L/S Standard
l__7__l Partition 2 1 = 3/1, 4/1 Radionics Standard
2 = 4/2 Ademco L/S Standard
3 = 4/2 Radionics Standard
6 = 4/2 Ademco Express
7 = Contact ID
8 = 3/1, 4/1 Ademco L/S Expanded
9 = 3/1, 4/1 Radionics Expanded
*49 Split/Dual Reporting l__0__l (0 = Backup Only)
To Primary Phone To Secondary Phone
1 = Alarms, Restore, Cancel All Other Reports
2 = All Reports except Open/Close, Test Open/Close, Test
3 = Alarms, Restore, Cancel All Reports
4 = All Reports except Open/Close, Test All Reports
5 = All Reports (Dual Reporting) All Reports
*50 15 sec Dial Delay l__0__l (0 = No, 1 = Yes)
*51 Periodic Test Message l__3__l (0=None, 1=24 Hrs, 2=Weekly, 3 = Monthly)
*52 Test Report Offset l__0__l (0 = Disabled, 1=6 Hours, 2=12, 3=18)
*53 Sescoa/Radionics l__0__l (0 = No, 1 = Yes)
*56 Zone Assignments (Max 24 hardwired and/or wireless zones in addition to the 8 onboard zones)
Hardwired Zone 01 to 08 (2-Wire Smokes Zone 1 only, 4-Wire can be 2 to 8)
4219/4229 Hardwire Expander Zone 10 to 17
Expander Trouble/Tamper Zone 09
Wireless Zone 10 to 63 (Depending on capacity of 5881 receiver)
Duress Zone 92
Fire Panic Zone 95
Medical Panic Zone 96
Police Panic Zone 99
1. Keypad displays "Zone Prog?" press 1
2. "Enter Zn No." enter which zone to program (01-87, 88-91, 95, 96, 97, 99) press *
3. Keypad will show summary zones programming, press *
4. "Zone Type?" enter zone type and press *
Common Zones Types
00 = Zone Disabled/Deleted 08 = 24 hour Aux/Medical
01 = Delay Zone 09 = Fire
02 = Secondary Delay Zone 10 = Interior Delay
03 = Perimeter/Instant 20 = Arm-Stay (RF only)
04 = Interior Follower/Motions 21 = Arm-Away (RF only)
05 = Trouble by Day/Alarm by Night 22 = Disarm (RF only)
06 = 24 hour Silent/Holdup 23 = No Alarm Response
07 = 24 hour Police Panic
5. "Partition?" Enter 1 or 2 then press *
6. "Report Code?" enter report code for zone
7. "Input Device?" Press 1 for Hardwired
2 Not Used
3 for Supervised RF (most sensors are RF)
4 for Un-Supervised RF
5 RF Button Type (Keyfobs/Panics etc)
6 Serial number polling loop devices
7 Dip Switch polling loop devices
8 Right Loop of DIP switch type device (4190 expander)
8. Cursor should flash above the loop number "LP#", Enter 1 to 4 depending on sensor
Door Switch - Internal switch loop 2, external connector loop 1
Glassbreak - Loop 1
Smoke Detectors - Loop 1 New version Vista-20S will ask for
Motions - Loop 1 Loop Number AFTER learning sensor
Keyfobs - Bottom Right Button = Loop 1
- Top Right Button = Loop 2 (Each button counts as 1 zone)
- Top Left Button = Loop 3
- Bottom Left Button = Loop 4
9. "Learn Sensor Y/N?" press 1 and trip sensor twice (you cannot enter serial numbers)
10. "Alpha Program?" press 0 if not programming Alpha descriptions
<CLICK HERE FOR ALPHA PROGRAMMING>
11. " Keypad will show either new summary for zone or "Enter zone number"
12. If finished programming enter 00 at "Enter zone no" to return to normal programming
Note: Serial numbers found on sticker on sensor, if not, learn by tripping sensor
*59 Exit Alarm Report Code l__0__l
*60 Trouble Report Code l__1__l__0__l (Fire Trouble)
*61 Bypass Report Code l__0__l__0__l
*62 AC Loss Report Code l__1__l__0__l
*63 Low Bat Report Code l__1__l__0__l
*64 Test Report Code l__0__l__0__l
*65 Open Report Code l__0__l Partition 1
l__0__l Partition 2
*66 Away/Stay Report l__0__l__0__l Partition 1
l__0__l__0__l Partition 2
*67 RF Xmtr Low Bat l__0__l__0__l
*68 Cancel Report Code l__1__l__0__l
*70 Alarm Restore Code l__0__l
*71 Trouble Restore Code l__0__l__0__l
*72 Bypass Restore Code l__0__l__0__l
*73 AC Restore Code l__0__l__0__l
*74 Low Bat Rest Code l__0__l__0__l
*75 RF Low Bat Rest Code l__0__l__0__l
*76 Test Restore Rpt Code l__0__l__0__l
*80 Output Relays (Usually program only if 4204 Relay is enabled in *25)
*81 Output Relays (Usually program only if 4204 Relay is enabled in *25)
*82 Custom Alpha Editing (Do not Program)
*83 Sequential Mode (Alternate way of programming sensors, not used)
*89 Event Log 80% Full l__0__l__0__l
*90 Event Logging l__0__l 0 = None
1 = Alarm/Restore
2 = Trouble/Restore
4 = Bypass/Bypass Restore
8 = Open/Close
*91 Option Selection l__0__l (0 = None, 4 = AAV)
Note: Make sure this is 0 to prevent Check 70 (Siren Supervision Trouble)
*92 Phone Monitor Enable l__0__l 0 = Not Used
Note: Panel MUST be properly grounded for this to work! 1 = KP Disp
2 = KP Disp/Sounder
3 = KP Disp/Sounder/Dev 2 starts
*93 Reports per Armed Period l__0__l 0 = 10 per Armed period
1 = Unlimited per Armed period
3=KP Display/Sounder/Device 2 starts
*94 Download Phone Number l__1__l__8__l__0__l__0__l__6__l__8__l__2__l__1__l__6__l__9__l__0__l
*95 Ring Count l__#_15_l (0 to 15 15 = Answer Machine)
*96 Reinitialize Download (No Value needed, keypad will just beep)
*97 Default Panel (No Value needed, keypad will beep and default panel)
*98 Exits Program Mode (Will not allow re-entry with Installer Code + 8 + 0 + 0)
*99 Exits Program Mode (Will allow re-entry with Code + 8 + 0 + 0)
Old 02-02-05, 11:56 AM
BVM
Thank You!
Thanks Brandon,
Your information was useful and exactly what I needed.
Bill