Vista 20P say's Fire Trouble 01

I just installed a System Sensor 2WT-B 2 wire Smoke Detector on zone 01 with zone type 09 and Reponse time 1 and I tried 2 too, and after leaving program mode my key pad beeps and say's Fire Trouble 01. What am I doing wrong. The Smoke Detector led's say's it's working normal green one lights after 5 sec. I have the pos wire connected to high and minus to low with EOLR on it. Only one Smoke Detector on system. What should I do?
 
Sponsored Links
  #2  
Old 06-08-05, 09:12 PM
Forum Topic Moderator
Join Date: Jun 2000
Location: Gainesville, FL, USA
Posts: 16,140
Upvotes: 0
Received 23 Votes on 22 Posts
For a smoke detector loop, the resistor has to be across the terminals of the last/only smoke in the loop. They are a normally open circuit.
 
  #3  
Old 06-08-05, 09:38 PM
JoeHack
Visiting Guest
Posts: n/a
Ok I think I get it. But

Ok, So I connect the EOLR accross the the smoke detector terminal + and - and not the alarm box terminal 9. Is that what I do?
 
  #4  
Old 06-08-05, 11:20 PM
Integratedj
Visiting Guest
Posts: n/a
Yes, that is all you need to do.
The smoke detector should have come with a small instruction page that will show you where if there are more than 2 terminals on the smoke.
IJ
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: