Announce-only zone type?

Hi all-

I thought I had everything figured out with regard to configurable zone type 90, on my Ademco/Honeywell Vista-20P system.

It may sound strange- but I would like to configure a zone type that does nothing more than chime at the keypad when the zone is activated and restored. I would like for it to chime (announce a 'change' via chime) during all modes (away, stay, night, disarmed). No alarm, no reports -just chime.

Using the configurable zone types worksheet, I configured *182 like so:
0 0 0 0 0 0 0 0 0 4

I successfully enrolled a 5816 loop 2 -using a zone type of 3 for testing. Worked perfectly...chimed as expected, displayed fault on the keypad, etc.

I then changed this zone's type to 90.
After doing so, I no longer got any faults displayed on the keypad- and, as you may have guessed- no chime

Any advice would be greatly appreciated.
Thanks,
John
 
  #2  
Old 10-20-06, 09:37 PM
M
Forum Topic Moderator
Join Date: Jun 2000
Location: Gainesville, FL, USA
Posts: 16,848
Received 116 Votes on 107 Posts
I think you need the sequence:
0 7 0 3 0 3 0 0 0 4

This tells it to fault in all arm/disarm conditions, with auto reset and chime when chime enabled. The zone fault will display on the keypad. The zone must fault to activate the chime.
 
  #3  
Old 10-20-06, 10:22 PM
J
Member
Thread Starter
Join Date: Sep 2006
Posts: 9
Received 0 Votes on 0 Posts
Got it!

Thanks again MrRonFL!

About 1 min. before I saw your reply, I tried:
0 3 0 3 0 3 0 0 0 4 -and thought I had it.

Seeing your reply and making the second digit a 7
-it now works exactly as a need.

Awesome!
 
 