Do smoke detectors and heat detectors connect to the same circuit?
Old 08-05-07, 01:59 AM
I am installing 4-wire smoke detectors, and two-wire heat detector (Kitchen) to a Power 832 system. Do these devices both connect to the same circuit? On the smoke detectors, I assume two wires are for power, and two are for detection. Would I use the detection wires for the heat detector?
Thanks,
Richard
Old 08-05-07, 08:09 AM
HotxxxxxxxOKC's Avatar
From just looking at the install manual you need to connect each of these detectors to each other, then have the last detector connected to a "Z" terminal on the board and the other on any "COM" terminal.
The two power wires will go to "AUX" and the other one to "PGM 1 or 2"
You will need a EOL resistor as well.
Here is the installer manual for your panel. Look at section 2.9.4
http://nextalarm.net/Files/5010im.pdf
I'm sure you will get more input soon as well.
Old 08-05-07, 04:38 PM
Received 24 Votes on 23 Posts
Yes, you may put the heat detector in the circuit. You would only use the alarm loop pair, of course. The heat detector is just a heat actuated normally open switch.
Old 08-07-07, 08:55 PM
Integrator97's Avatar
You should also have a power supervision relay connected at the last smoke detector. THis monitors the power on a 4 wire smoke loop, and if the power goes away, breaks the detector or zone circuit, causing a trouble.