Old 06-01-08, 09:11 PM
A
Member
Thread Starter
Join Date: Jun 2008
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
PC 1616 giving me Trouble #4 FTC

I just finished installing a PC1616 and I have it set up as a local alarm only, no communication. I am getting trouble #4, failure to communicate. So far I have all 3 telephone numbers programmed as all zeros; and i have [380] off. What is it that's causing this? Thank you.
 
  #2  
Old 06-02-08, 04:32 AM
M
Forum Topic Moderator
Join Date: Jun 2000
Location: Gainesville, FL, USA
Posts: 15,361
Received 267 Upvotes on 246 Posts
Not zeros, HEX F should be in all of the phone number slots.

Also, one quirk of DSC panels is that the telephone trouble will often not clear until you power cycle (reboot) the panel.
 
  #3  
Old 06-02-08, 02:12 PM
T
Member
Join Date: Mar 2008
Location: Canada
Posts: 90
Upvotes: 0
Received 0 Upvotes on 0 Posts
you will also have to got to section 015 in programming and make sure that 8 is off. and then like ron said, reboot your panel.
 
 