DSC Power 832 / PC5010 calling issues
Hello!
I have this system installed in our warehouse, although it hasn't been used for several years. I've been given the responsibility of getting this system up & running for local protection only without the monitoring service.
I have the installers manual & have gotten almost everything where we need it. I reprogrammed the communicator to call my cell during testing. It does call my cell, but it never stops. My guess is it's looking for a kiss off signal from the monitoring station. I guess I'd like to know if there's a way I can prevent this system from attempting to "check in" with the central station, but still allow the communicator to function as a dialer. (I do get a trouble light, "failed to communicate")
I've spent a few days reading these forums in attempt to refrain from asking a question that has probably been asked before, but I haven't found what I'm looking for.
Thanks for any input!
I have this system installed in our warehouse, although it hasn't been used for several years. I've been given the responsibility of getting this system up & running for local protection only without the monitoring service.
I have the installers manual & have gotten almost everything where we need it. I reprogrammed the communicator to call my cell during testing. It does call my cell, but it never stops. My guess is it's looking for a kiss off signal from the monitoring station. I guess I'd like to know if there's a way I can prevent this system from attempting to "check in" with the central station, but still allow the communicator to function as a dialer. (I do get a trouble light, "failed to communicate")
I've spent a few days reading these forums in attempt to refrain from asking a question that has probably been asked before, but I haven't found what I'm looking for.
Thanks for any input!
#3
Member
Thread Starter
Join Date: Oct 2008
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
My installer's manual is rather vague. There's a section that decribes the pager format & mentions the programming is in section [360], but it doesn't go into any further detail. I searched these forums & here's what I came up with:
*8 (installer's code)
[301] (telephone number) *6*#
[360] 05 02
[380] #1 "on"
In this mode, I no longer get random calls. However, when I trip the alarm it continues to call over & over. I have [160] set to 002 (2 calls max), but that command is ignored & the system constantly dials out. Originally section [360] was set to 03 02. I'm not sure what that means exactly since my manual doesn't contain such information. I'm getting closer, but not quite there. Thanks again for any help
*8 (installer's code)
[301] (telephone number) *6*#
[360] 05 02
[380] #1 "on"
In this mode, I no longer get random calls. However, when I trip the alarm it continues to call over & over. I have [160] set to 002 (2 calls max), but that command is ignored & the system constantly dials out. Originally section [360] was set to 03 02. I'm not sure what that means exactly since my manual doesn't contain such information. I'm getting closer, but not quite there. Thanks again for any help
#4
Forum Topic Moderator
The PC 5010 is rather annoying in that there is a separate programmiing sheet booklet, and without both books the programming instructions are cryptic at best.
Search for that one as well.
Your programming should be:
301 [phone number] *6*
360 05 03 (the second slot actually doesn't matter)
361 thru 368 only option 1 on
380 option 1 on
You may have to power the panel down and restart it to clear the old dialer configuration fully (it's a DSC quirk).
Search for that one as well.
Your programming should be:
301 [phone number] *6*
360 05 03 (the second slot actually doesn't matter)
361 thru 368 only option 1 on
380 option 1 on
You may have to power the panel down and restart it to clear the old dialer configuration fully (it's a DSC quirk).