A question about 2,000 ohm resistor at end of line for Concord

Why does it have to be at end of line,every think you read says that. Why can't the resisters just be a single point all together (on different lines,in one place). One wiring diagram shows resistor on ground side of last contact and another diagram shows on the positive side of the last contact. Does the concord use the resistor to measure the end of the circuit like a fault meter or bridge set would for a trouble in a line. Just wondering WHY?
 
Sponsored Links
  #2  
Old 09-14-14, 01:20 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,230
Received 379 Votes on 356 Posts
Ahhh.... the poor misunderstood end of line resistor.

It's actually used to monitor the line and as an aid. If the resistor is installed at the panel and the zone is shorted just outside the panel..... you'd never now. The zone would show normal but would not respond. By putting the resistor at the last device.... any short in the wiring would be detected as a fault.

The EOL resistor just needs to be at the last device. It doesn't matter if it's in the + or - line.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: