Vista 20p notification appliance supervision

I have a vista 20p with a relay connected to a Wheelock strobe sync module then going out to 5 horn/strobes. There must be a way to supervise them. I was thinking with maybe another relay, EOLR and an additional zone set to 24hr aux but I can't figure out how to do it.

Thanks,
Jason
 
Sponsored Links
  #2  
Old 08-23-16, 07:02 PM
Forum Topic Moderator
Join Date: Jun 2000
Location: Gainesville, FL, USA
Posts: 16,173
Received 28 Votes on 27 Posts
Sending the power out through a relay like that, there's really no way to create a supervised circuit, since you aren't providing the reverse polarity supervision voltage that would be created by a normal supervised notification device circuit.

If you are trying to get this to meet AHJ compliance, there's no way to mickey-mouse a solution that would actually meet muster.

Your best bet is to get an inexpensive listed NAC power supply.
 
  #3  
Old 08-23-16, 09:14 PM
Member
Thread Starter
Join Date: Oct 2015
Posts: 48
Received 0 Votes on 0 Posts
This is for a residential installation. The owner has horn strobes connected to the vista 20p and activated by a relay. I wanted to see if there was a way to "supervise" the loop of them by some means to be notified in case of a wire cut or an issue with one of them causing power not to flow through and get to the rest. I figured there could be some way to do this. Since it's in a residence, there will be no inspection and I figured some type of supervison is better than nothing since all 2 and 4-wire smokes on the system are.
 
  #4  
Old 08-26-16, 02:58 AM
Member
Thread Starter
Join Date: Oct 2015
Posts: 48
Received 0 Votes on 0 Posts
Does anyone have any more information on this? Thanks.
 
  #5  
Old 09-15-16, 03:43 AM
Member
Thread Starter
Join Date: Oct 2015
Posts: 48
Received 0 Votes on 0 Posts
I am getting a NAC power supply for this that's compatable with the horn/strobes and will provide supervision. However, I just came across the 4204cf; a supervised NAC output relay. I'm just curious at this point if this compatable with the vista 20p? Thanks.
 
  #6  
Old 09-15-16, 02:36 PM
Forum Topic Moderator
Join Date: Jun 2000
Location: Gainesville, FL, USA
Posts: 16,173
Received 28 Votes on 27 Posts
Sadly, no. Per Honeywell, it is compatible with the commercial panels like a Vista-128, or a Vista-250, but not any of the residential panels, like a 15p or 20p.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: