Vista 20p sounder output question

Strange request...is there a way to make the sounder output (terminal 3) steady for fire alarms instead of pulsed? I am using relays to different devices and need continuous for fire and burg. Thanks
 
Sponsored Links
  #2  
Old 09-05-16, 07:23 PM
Forum Topic Moderator
Join Date: Jun 2000
Location: Gainesville, FL, USA
Posts: 16,331
Received 38 Votes on 37 Posts
That's a hardwired function on V20p panels. To get a steady output, you would need to use the output connector, and program an output to turn on steady in alarm.
 
  #3  
Old 09-05-16, 07:30 PM
Member
Thread Starter
Join Date: Oct 2015
Posts: 54
Received 0 Votes on 0 Posts
Thank you. What do you mean by output connector? The auxiliary power output?
 
  #4  
Old 09-06-16, 03:08 AM
Forum Topic Moderator
Join Date: Jun 2000
Location: Gainesville, FL, USA
Posts: 16,331
Received 38 Votes on 37 Posts
The specific name is the onboard trigger connectors. See page 2-11 in the installation manual: http://www.nationwidesecuritycorp.co...all-Manual.pdf
 
  #5  
Old 09-06-16, 08:52 AM
Member
Join Date: Sep 2015
Location: US
Posts: 406
Received 7 Votes on 6 Posts
Also, take note of the current limitations on these outputs.
 
  #6  
Old 09-07-16, 03:19 AM
Forum Topic Moderator
Join Date: Jun 2000
Location: Gainesville, FL, USA
Posts: 16,331
Received 38 Votes on 37 Posts
If the primary goal is triggering relays; the outputs are definitely the way to go, that is going to be a low current application.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: