Vista 20P zone Faults Won't Clear
#1
Member
Thread Starter
Join Date: Sep 2019
Posts: 7
Received 0 Votes
on
0 Posts
Vista 20P zone Faults Won't Clear
hello everyone
I have replaced my old VISTA 20P with a brand new VISTA 20P but unfortunately i'm getting fault message zone 4 and 5 both (PIR) and some times zone 6 . i couldn't clear that by entering the master code nor by the installer code.
I have replaced my old VISTA 20P with a brand new VISTA 20P but unfortunately i'm getting fault message zone 4 and 5 both (PIR) and some times zone 6 . i couldn't clear that by entering the master code nor by the installer code.
#4
How are the zones wired? Are they using EOL's (End Of Line Resistors) either at the control panel or at the sensors? How are the zones programmed? If the zones use EOL's and you programmed them as Hardwire Type 1 NC (Normally Closed) it's going to cause a problem. Zones using EOL's must be programmed as Hardwire Type 0-EOL.
Also verify the motion detectors are operating properly and receiving power.
What do you have on zone 6?
Also verify the motion detectors are operating properly and receiving power.
What do you have on zone 6?