Swamp cooler - water valve electrical connection.


jbrentpoer's Avatar
Member

Join Date: Sep 2017
Posts: 4

09-18-17, 03:01 PM   #1 (permalink)  
Swamp cooler - water valve electrical connection.

Hello! I have question related to controlling the water flow to my Swamp cooler. Iím new to this site, so hopefully Iím in the right forum.

This is a basic swamp cooler that has two switches on the control panel. One switch controls the water pump and the other controls the fan.

I would like to have the existing switch for the swamp cooler pump also control a solenoid valve located at the water source. The goal is to not have any pressurized water in the small ľ inch line running to the swamp cooler when it is not on. My experience is that even with the best quality equipment, this small line is prone to damage and failure. Iíd like to limit these issues by shutting the water off at the source, anytime the unit is off.

Question: Can I just connect the wires from the 110v Swamp Cooler pump to my normally-closed 110v solenoid valve to turn the water on and off?

Thank You!
jbrentpoer

 
Sponsored Links
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,171
NJ

09-18-17, 03:36 PM   #2 (permalink)  
Welcome to the forums.

You'll find your thread now in the evaporative cooler forum.

I'm a little lost.... are you adding a second 120v solenoid to the system ?
If there is one inside the unit.... it should already turn off when the unit is off.


~ Pete ~

 
jbrentpoer's Avatar
Member

Join Date: Sep 2017
Posts: 4

09-18-17, 03:48 PM   #3 (permalink)  
Thank you for moving this to the proper forum.

Yes, I am adding a 120v solenoid valve located away from the swamp cooler at the water source.

jbrentpoer

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,171
NJ

09-18-17, 03:56 PM   #4 (permalink)  
Ok.... I see no problem having the cooler itself activate the remote valve but the wiring needs to be kept acceptable for 120vac wiring. I would also put an inline fuse inside the cooler to protect the outgoing line. Something around 3A would be ok.


~ Pete ~

 
ray2047's Avatar
Group Moderator

Join Date: Mar 2006
Posts: 32,032
TX

09-18-17, 04:02 PM   #5 (permalink)  
To make wiring to the source of water easier I'd suggest a 24 volt coil and an auxiliary transformer at the cooler. Less code requirements for 24 volt wiring.


I can explain it to you, but I can't understand it for you.

 
jbrentpoer's Avatar
Member

Join Date: Sep 2017
Posts: 4

09-18-17, 04:35 PM   #6 (permalink)  
I like the idea of a 24V Relay & Transformer. That would really simplify getting the wire to a 24V Solenoid.
Does it still make sense to use the evaporative cooler pump as the power source for the Transformer?

Is a fuse needed in with this scenario? If so, where?

Thank You!

jbrentpoer

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,171
NJ

09-18-17, 05:01 PM   #7 (permalink)  
If you use a small 120v > 24vac transformer you won't need a fuse.
The transformer is internally protected.
Yes.... you can use the pump circuit.


~ Pete ~

 
jbrentpoer's Avatar
Member

Join Date: Sep 2017
Posts: 4

09-18-17, 05:11 PM   #8 (permalink)  
Thanks All! The folks on this forum are super helpful!