Fireplaces
Old 02-12-03, 08:45 PM
piglet
Fireplaces
I recently removed the tile that the former owner had installed over the red brick on the fireplace. Unfortunately, alot of the brick came off with the tile, as well as a lot of the cement/glue that was used to hold the tiles in place.
To cover the brick, is it possible to install some form of plaster (or something similar) that would allow texture to be added?
Old 02-13-03, 06:38 AM
Doug Aleshire's Avatar
piglet,
Easiest way would be to install a cement board backer material to face of fireplace. Apply with TapCon screws. Then you could apply whatever type surface you wanted. A stucco application is one way or to apply cultured stone or tile with the use of thin set mortar.
http://www.culturedstone.com/technical/
You can also do a search on the forum for stucco applications as well.
Current Codes on fireplaces;
R1003.9.1 Hearth Thickness - The minimum thickness of firepalce hearths shall be 4" thick. (102)
R1003.9.2 Hearth Extension Thickness - The minimum thickness of hearth extension shall be 2" (51 mm)
Exception; When the bottom of the firebox opening is rasised at least 8" (203mm) above the top of the hearth extension, ahearth extension of not less than 3/8" inch thick (9.5mm) brick, concrete,stone, tile,or other approved noncombustible material is provided.
R1003.10 Hearth Extension Dimensions - Hearth extensions shall extend at least 16 inches (406mm) in front of and at least 8 inches (203mm) beyond each side of the fireplace opening. Where the fireplace opening is 6 square feet (0.557m2) or larger, the hearth extension shall extend at least 20 inches (508mm) in front of and at least 12 inches (305mm) beyond each side of fireplace opening.
R1003.12 Fireplace Clearance - All wood beams, joists, studs and other combustible material shall have a clearance of not less than 2 inches (51mm) from the front faces and sides of masonry fireplaces and not less than 4 inches (102mm) from the back of masonry fireplaces. The air space shall not be filled except to provide fireblocking in accordance with Section R 1003.14.
Exceptions:
1. Masonry fireplaces listed and label for use in contact with combustibles in accordance with UL 127 and installed in accordance with the manufactures installation instructions are permitted to have combustible material in contact with their exterior surfaces.
2. When masonry fireplaces are part of masonry or concrete walls, combustible materials shall not be in contact with the masonry or concrete walls less than 12 inches (305mm) from the inside surface of the nearest firebox lining.
3. Exposed combustible trim and edges of sheathing materials such as wood siding, flooring and drywall shall be permitted to abut the masonry fireplace sidewalls and hearth extension provided such combustible trim or sheathing is a minimum of 12 inches (305mm) from the inside surface of the nearest firebox lining.
4. Exposed combustible mantels and trim may be placed directly on the masonry fireplace front surrounding the fireplace opening providing such combustible materials shall not be placed within 6 inches (152mm) of a fireplace opening. Combustible material within 12 inches (306mm) of the fireplace opening shall not project more than 1/8 inch (3.2mm) for each 1-inch (25.4mm) distance from such opening.
Hope this helps!