Ignition Control Bad?

My automatic gas fireplace just quit. Looking close, the pilot lights for 1-2 seconds then all shuts down. Looking closer, with a voltmeter, I get no voltage from the terminals on the Honeywell S8600H ignition control. Also no voltage at the M & C terminals on the gas valve. Is my ignition control bad, even tho the pilot lites?

Thanks in advance.
 
  #2  
Old 11-29-12, 10:13 AM
R
Member
Thread Starter
Join Date: Nov 2012
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Update: I isolated the transformer and am getting 24VAC, so that's OK. Igniter is sparking. Would appreciate any help from here.
 
  #3  
Old 11-30-12, 01:33 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,166
Received 1,525 Votes on 1,408 Posts
Could be defective ignition module although there are several small issues that could cause the module to appear defective. I left you a link to the tech service manual and troubleshooting info for your module. Your ignition module should also have diagnostic lights on it and page 20 goes into depth.




http://www.forwardthinking.honeywell...ll/69_1955.pdf
 
  #4  
Old 12-13-12, 12:59 PM
R
Member
Thread Starter
Join Date: Nov 2012
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Smile All fixed

Thanks for the info on the status light. It showed a controller fault. Replaced the controller and all is well.
 
 