Help Sizing Beam
Help Sizing Beam
I would like to replace a load bearing wall in my basement with a beam and need some help sizing the beam. The span is 19' and the distance on one side is 12' and the other side is 7' which gives me a total tributary width of 9'. The space above is a living room with hardwood floors. The house has 2 stories above the basement, but this span is only supporting the one floor above. I was thinking I would use LVL's, but am open to other suggestions. The living room above has the exact same span condition with a beam spanning the same distance to support the top floor and that beam isn't any thicker than 3.5", but it is encased in drywall and I don't know what it is made of. Since I would be duplicating this in the basement I would assume I could get by with (2) 18" deep LVL's, but would like to know for sure.
Any help would be greatly appreciated.
Thanks,
Paul
Thanks,
Paul
Help Sizing Beam
Get an engineer to save you some money.
He will also be able to give you a design for the footings under the bearing points for the beam. the wall you are replacing probably does not have a proper footing for the load the beam will be carrying (LL + DL).
Even if you do it yourself without a permit, you will have a design to show the future purchaser that it was not just a "patch job".
Dick
Dick
Please check Calc's
I think I found my answer here http://www.rfpco.com/pdfs/EWP_DG/Lvl.pdf
According to their instructions and tables, I have to use a longer tributary length because my I-Joists are continuous so the calculations are 50PSF x 12.25 x 1.25 which gives me a total PLF load of 766 and a 2-ply 18" LVL will span my 19' distance.
I would really appreciate it if someone can tell me if I did this right though.
Thanks,
Paul
Thanks,
Paul
first, (2) 18" lvl's won't make that span according to those tables and the load information you provided. The same is true for my software. (3) 16" lvl's will work--according to your numbers.
BUT you need someone to verify that those numbers are sufficient to suit your situation; to make sure there isn't anything else going on underneath the surface that you haven't picked up on. This is a big project, also probably not a diy.
And as previously mentioned you'll need footings under the bearing points, because there will be nearly 7500 lbs. coming down off each end of that beam.
The biggest point not to miss here is what the other two guys said above....766plf over 19' = 7,277lbs on each support at the ends. The load-bearing wall distributes the 14,000+ load across it's length and any basement slab will easibly support that being transferred through the bottom plate....but it's a different story when that becomes a point load on the ends.
Change of Plans
Rather than replacing the wall with a single beam, I've decided to do it in smaller 6' segments so I'll have several columns. This will make it a lot more manageable for me to do it myself, save some money and alleviate the footing problem. There is already one 6' opening and I can do the other two one at a time to minimize the temporary bracing.
Thanks for all the replies.