14' wall height framing material reqm't per 2006 International Building Code


fvfarms's Avatar
Member

Join Date: Dec 2017
Posts: 2

12-29-17, 07:24 AM   #1  
14' wall height framing material reqm't per 2006 International Building Code

My county uses the 2006 International Building Codes

We are building a 40' x 54' garage

The materials calculator we used at the home improvement store is saying 2x4 walls on 16" centers

The wall height will be 14'

I compared this plan to the above referenced building code, but I am an amateur and I'm not sure if I'm reading correctly. However, it appears to me that a load bearing wall of 14' height requires 2x6 construction per the above referenced code. Is this accurate? Or is the 2x4 given on the plan acceptable?

Also, we are zone 4 (midwest) on the energy efficiency map which looks like we need the R19 value of insulation provided by the 2x6 construction.

Any experience or suggestions would be greatly appreciated as everyone who sells materials only wants to direct me to an engineer. I'm just trying to do a preliminary budget to see if 2x4 or 2x6 is what we have to use so I'm not ready to consult an engineer yet.

Thank you

 
Sponsored Links
stickshift's Avatar
Group Moderator

Join Date: Oct 2004
Posts: 18,476
WI

12-29-17, 07:42 AM   #2  
I would call the local AHJ, they're the group you have to make happy in the end anyway.

 
Handyone's Avatar
Forum Topic Moderator

Join Date: Aug 2000
Posts: 5,451
CAL

12-29-17, 08:33 AM   #3  
Welcome.
There are many factors in building a garage so it will take some research on your part to make acceptable plans.
If all you want to do is estimate the cost here's a few suggestions to make it somewhat easier:
- estimate the trusses, roof and wall sheathing and all other material that won't change whether it's 2 x 4 or 2 x 6.
- estimate the 2 x 4 walls at 16" on center and estimate the 2 x 6 walls at 24" on center.
I don't know of any reason the walls would need to be 2 x 6, but as said you need to find out for sure.


Brian
Cal Contractor

 
XSleeper's Avatar
Group Moderator

Join Date: Dec 2004
Posts: 19,285
NE

12-29-17, 10:47 AM   #4  
The footnote (a) to table 602.3.(5) says in part, "Increases in unsupported height are permitted where
justified by analysis." So basically if you want to use a 2x4 wall taller than 10', you need a structural engineer to say it's okay... in addition to the load, they take things like wind load into play, which affects walls that are not laterally retrained.

I would save myself the headache and just use 2x6 as the code mentions. As you mentioned, you need it anyway to get to R19.

 
fvfarms's Avatar
Member

Join Date: Dec 2017
Posts: 2

01-01-18, 06:43 AM   #5  
Thank you everyone. I appreciate the info

 